I'm considering building a preheater for my furnace's combustion air. Winter is almost over so unless weather gets weird it might not be a factor until the fall. I currently have 2x 50kbtu natural gas furnaces with 80% afue existing in the same attic space. This attic space has a super insulated floor and 3-4 layers of radiant barrier and a ridge vent. Something I always notice is the roof above the adjacent attic space will frost while this one doesn't. Seems like there is a lot of heat energy left in the 20% going out the flue. Because of our short and warm winters 80% furnace are the norm and I have 5-10yrs left on my equipment's life span.

I have found a few papers on using combustion preheaters to increase industrial equipment efficiency and possibly reduce some emissions. On a small scale it might not do much, but as we know here gaining 1-2% overtime adds up. My current plan is to wrap my 4" flue double wall type b vent with 6" single wall snap, nearest to furnace connect a 4-4-6 wye and feed 4" aluminum flex into my furnace. My Ruud unit has a stub for a combustion air duct. As the furnace burns it will draw fresh air from the 6" pipe wrapped around the flue. If I really want to go all the way I could replace the double wall 4" with single wall, this pipe gets way hotter. Double wall flue clearance is 1" from combustibles vs 4-5" for single wall.
http://energy.gov/sites/prod/files/2..._preheated.pdf
http://energy.gov/sites/prod/files/2..._preheated.pdf

__________________
1.47 kw solar, R-40+ attic insulation, 4 layers radiant barrier, solar attic fan, solar mini pool pump
gtojohn is offline   Reply With Quote
Old 03-01-16, 11:06 AM   #2
gtojohn
Journeyman EcoRenovator
 
gtojohn's Avatar
 
Join Date: Jul 2014
Location: Austin, TX
Posts: 314
Thanks: 39
Thanked 50 Times in 45 Posts
Default

single wall wye
__________________
1.47 kw solar, R-40+ attic insulation, 4 layers radiant barrier, solar attic fan, solar mini pool pump
gtojohn is offline   Reply With Quote
Old 03-01-16, 11:17 AM   #3
Mobile Master Tech
Apprentice EcoRenovator
 
Mobile Master Tech's Avatar
 
Join Date: May 2012
Location: Atlanta, Ga
Posts: 142
Thanks: 38
Thanked 41 Times in 34 Posts
Default

GTO,

There will be some efficiency to gain, but I see a few hurdles.

One, even if your furnaces have combustion blowers, they are still draft furnaces requiring certain flue attributes as described HERE. Be mindful of the requirements of other devices, like water heaters, that share a flue. You wouldn't want to create negative draft conditions that might invite carbon monoxide in the house!


If you lower the flue discharge temp, you are likely to get more corrosion of the flue since more condensation will occur and the flue won't be as hot at shutoff to reevaporate it.


You probably aren't going to take an unacceptable amount of heat away from the flue with the short section you describe, but you will certainly change the air/fuel ratio of the furnaces, since they will be drawing through a restriction instead of free air, and the inlet pressure your furnaces see will be lower still as the combustion air is trying to rise out of the inlet since it is now warmer and buoyant. The same volume of air now has fewer molecules of oxygen since it is warmer. If you do this, be sure the furnace runs at stoichiometric under all operating conditions.

Lastly, you will gain WAAAAYYYY more efficiency by relocating equipment and as much ductwork as possible into conditioned spaces (even building a conditioned space around them), or replacing with more efficient systems if you can. There is a frighteningly large amount of air leakage in equipment casings and air ducts, plus so much surface area to lose/gain heat through even if it is well sealed.

I removed both my furnaces and installed hydronic retrofit heat plate warm floors powered by a 95% efficient water heater, plus a 23SEER Nordyne inverter air conditioner which can vary its output from 1.5 to 3.5 tons, allowing one unit to cool the whole house. Rearranging the ducts to do this got all my equipment out of the attic and reduced the amount of ductwork in unconditioned space by half.

Even though I was now heating/cooling 3 floors AND a garage instead of just 2 floors in a 5br/3.5ba house, the cooling demand for kwh went down to 15kwh/day from around 60kwh/day, and my gas use during heating season went from 300-350 therms/mo to 175-225/mo.
__________________
"I‘d put my money on the sun and solar energy. What a source of power! I hope we don‘t have to
wait until oil and coal run out before we tackle that." Thomas Edison, 1847 — 1931

Last edited by Mobile Master Tech; 03-01-16 at 11:19 AM.. Reason: Typo
Mobile Master Tech is offline   Reply With Quote
The Following User Says Thank You to Mobile Master Tech For This Useful Post:
Servicetech (03-13-16)
Old 03-01-16, 07:22 PM   #4
JRMichler
Apprentice EcoRenovator
 
Join Date: Apr 2012
Location: Phillips, WI
Posts: 109
Thanks: 10
Thanked 30 Times in 25 Posts
Default

Quote:
Originally Posted by gtojohn View Post
Something I always notice is the roof above the adjacent attic space will frost while this one doesn't.
Frost on the inside of a roof is due to warm moist air leaking from the conditioned space. Fix those air leaks (there is always more than one) and you will save much more than by preheating furnace intake air.

I replaced an 85% efficient water heater hydro air system with a 95% efficient boiler with indirect water heater. My gas consumption decreased 24% for the same number of degree days.
JRMichler is offline   Reply With Quote
The Following User Says Thank You to JRMichler For This Useful Post:
Servicetech (03-13-16)
Old 03-02-16, 06:04 AM   #5
Mobile Master Tech
Apprentice EcoRenovator
 
Mobile Master Tech's Avatar
 
Join Date: May 2012
Location: Atlanta, Ga
Posts: 142
Thanks: 38
Thanked 41 Times in 34 Posts
Default

The 6" around the 4" isn't going to be enough flow area either, and 4" supply duct may not be enough. Manufacturer and code requirements differ but you will probably want to go with the most conservative NFPA 54 requirement of 1sqin of air opening per 2000btu of burner unless you carefully research otherwise, 20sqin per furnace in your case. The area between a 6" pipe and a 4" is about 6.5sqin, and the area of a 4" duct is 12.5sqin.

If you move or replace equipment, make sure to provide external combustion air or have sealed burners that draw only outside air for combustion. The draft caused by drawing in cold air to replace combustion air wastes a lot of heat, and could risk CO poisoning if your house was tightly sealed.
__________________
"I‘d put my money on the sun and solar energy. What a source of power! I hope we don‘t have to
wait until oil and coal run out before we tackle that." Thomas Edison, 1847 — 1931
Mobile Master Tech is offline   Reply With Quote
Old 03-02-16, 08:49 AM   #6
gtojohn
Journeyman EcoRenovator
 
gtojohn's Avatar
 
Join Date: Jul 2014
Location: Austin, TX
Posts: 314
Thanks: 39
Thanked 50 Times in 45 Posts
Default

Frost was on the outside, on top of the shingles above the attic without furnaces. Attic space with furnaces, no frost on the shingles. My ducts are reasonably tight, lots of mastic, rebuilt 2 plenums when I moved one for a remodel last year. Again its warm here, my January gas usage was high at 86 therms compared to December's 52 therms. Saving 2% on $30 worth of gas won't do much for me, its more of an experiment for a cheap improvement. Maybe a feather in my cap. Both heaters are power vented with their own dedicated runs. I don't think there will be much of a restriction for the combustion air, 2" pipe is all 50kbtu furnaces need. The ruud installation manuals always show this as an installation option in tight or restricted spaces. The factory concentric vent kits for the 90%+ furnaces use a similar idea, flue gas in a center pipe while outside combustion air flows around it in an outer jacket. And the combustion air pvc pipes are also 2" on the 90% 50k and 70 kbtu units. Because my heaters are in the open attic cold air draft from combustion make up aren't really a problem.
t.
__________________
1.47 kw solar, R-40+ attic insulation, 4 layers radiant barrier, solar attic fan, solar mini pool pump
gtojohn is offline   Reply With Quote
The Following User Says Thank You to gtojohn For This Useful Post:
jeff5may (03-05-16)
Old 03-02-16, 10:14 AM   #7
Mobile Master Tech
Apprentice EcoRenovator
 
Mobile Master Tech's Avatar
 
Join Date: May 2012
Location: Atlanta, Ga
Posts: 142
Thanks: 38
Thanked 41 Times in 34 Posts
Default

You should be good with your heat exchanger idea since you have separate runs for each, as long as the units are designed to use a more restrictive metal coaxial air/flue combination. You mentioned 80% efficiency, so I wasn't sure if they were the type of non-condensing power burners which might need the flue to act like a draft flue as described in the link I posted.

90%+ efficiency furnaces condense, therefore exhaust temps are lower and most can vent through plastic pipe. Those burners are designed for that restriction.

True, you only need outside combustion air provisions if you move the units into enclosed or conditioned space.
__________________
"I‘d put my money on the sun and solar energy. What a source of power! I hope we don‘t have to
wait until oil and coal run out before we tackle that." Thomas Edison, 1847 — 1931
Mobile Master Tech is offline   Reply With Quote
Old 03-05-16, 05:00 PM   #8
oil pan 4
Land owner
 
Join Date: Nov 2012
Location: NM
Posts: 1,026
Thanks: 12
Thanked 127 Times in 107 Posts
Default

My mechanical engineer buddy got one of those condensing higher heating value 100,000BTU/hr natural gas furnaces that can be vented through PVC, one that can be installed in a trailer home. He opted to install his new furnace trailer style in the basement of his house, where the furnace draws air from out side the house.
That way the furnace is not drawing air from inside the house, which intern does not draw cold air into the house.
I think that would be the bigger efficiency improvement as compared to prewarming the air.
oil pan 4 is offline   Reply With Quote
Old 03-07-16, 09:05 AM   #9
gtojohn
Journeyman EcoRenovator
 
gtojohn's Avatar
 
Join Date: Jul 2014
Location: Austin, TX
Posts: 314
Thanks: 39
Thanked 50 Times in 45 Posts
Default

yes combustion air from outside the conditioned space is definitely the way to go. Each Cubic foot of gas requires 10 cubic feet of air, so 100kbtu would exchange all the air in your house several times over. Thats why outside combustion air is part of the energy code. Mine are located in the unconditioned open air attic crawl space so there's no loss there. What I suggest is preheating the combustion air which presumably you are bring in from outside, which is colder because you are running the heater. You already have a flue and need combustion air why not preheat it? Testing a double wall flue last week, 3' from the furnace still very hot, couldn't keep my hand on it. about 4' from it it was warm to touch, maybe 100-105f. If I wanted to get max heat out of it I'd use single wall vent. Unfortunately winter's over here, my hvac has been off for almost a month, so might not happen for me until fall. Maybe someone in a colder climate might want to try it before then.
__________________
1.47 kw solar, R-40+ attic insulation, 4 layers radiant barrier, solar attic fan, solar mini pool pump
gtojohn is offline   Reply With Quote
Old 03-13-16, 11:11 AM   #10
Servicetech
Apprentice EcoRenovator
 
Servicetech's Avatar
 
Join Date: Nov 2013
Location: Moore Oklahoma
Posts: 267
Thanks: 108
Thanked 23 Times in 21 Posts
Default

85% That's the MAXIMUM efficiency you can get out of a non-condensing gas appliance. The other 15% of the combustion process is latent heat, and you must condense the combustion gasses to capture it. The 5% difference between 80% furnace and the maximum 85% theoretical non-condensing efficiency allows a safety margin so flue gases don’t condense.

Combustion Efficiency and Excess Air

Mobile Master Tech is SPOT ON with his advice.

Servicetech is offline   Reply With Quote
The Following User Says Thank You to Servicetech For This Useful Post:
gtojohn (03-15-16)
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 09:51 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design