Default BTU calculation

Anybody have a quick formula to calculate BTUs that I'm getting from the well water in my open loop GSHP? Entering water temp is 52 F, and discharge temp is about 38 F, pumping 12 GPM.

Thanks.

Mike

Myoungmike is offline   Reply With Quote
Old 01-28-11, 05:09 PM   #2
RobertSmalls
Journeyman EcoRenovator
 
RobertSmalls's Avatar
 
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
Default

Simple.

Heat flux equals mass flow rate times specific heat times change in temperature.
Q' = m' * K(H2O) * deltaT
Q' = 12gal/min*8(lb/gal)*4.2kJ/(kg*K)*(52°F-38°F)

Drop that whole line minus the Q'= into Wolfram Alpha, and it spits out the answer in any unit you like.
12gal/min*8(lb/gal)*(4.2kJ/(kg*K))*(52°F-38°F - Wolfram|Alpha)

81000BTU/hr, or 24kW.
RobertSmalls is offline   Reply With Quote
Old 02-26-11, 08:12 AM   #3
mrd
Apprentice EcoRenovator
 
Join Date: Feb 2010
Location: Milford, DE
Posts: 106
Thanks: 5
Thanked 9 Times in 9 Posts
Default

While doing some reading, I wondered how effective a solid metal heat pipe would be at transferring heat, instead of pumping fluid around. I threw some numbers together. Just a silly exercise, but I thought I'd throw it on this thread for kicks.

I found this formula for conductive heat transfer:
Q = k A dT t / L

dT temp diff
t transfer duration
A cross sectional area
L length
k thermal conductivity, J / (s m degreesC)

I found the thermal conductivity of aluminum = ~120 btu/(hr ft degreesF)
I converted it to ~208 watt/meter/K, which is equivalent units to k above.

I decided to see numbers for meeting a 20kbtu/h load.
20kbtu/h / 3.414 = ~5860 J/s

Q = k A dT t / L
Q / t / k = A dT / L
5860 / 208 = A dT / L
28.17 = A dT / L

From this I made a spreadsheet to see the required cross-sectional area of aluminum pipe to handle a given dT and length



length in meters, delta T in celcius, and the resultant data is the diameter of solid heat pipe, in inches. The smallest is a 2 foot diameter pipe, a mere 1 meter long, with a deltaT of 1000 degrees C, to just meet a 20kbtu/h load ..

I wonder if I did something wrong, that seems ludicrous.
Attached Thumbnails
Click image for larger version

Name:	untitled.JPG
Views:	7885
Size:	63.3 KB
ID:	1292  
mrd is offline   Reply With Quote
Old 02-26-11, 08:31 AM   #4
RobertSmalls
Journeyman EcoRenovator
 
RobertSmalls's Avatar
 
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
Default

I think you did something wrong. I did the following calculation:

Let k=200W/m*K, A=1m², l=1m, q'=6kW.
Find dT.
q'=k*A*dT/l
6000W=200W/(m*K)*1m²*dT /1m
30K=dT

So for each meter that you have to move 6kW through a 22.2" diameter Al rod, you need 54°F temperature differential. Mass transfer is a dramatically more effective way to move heat than conduction. Speaking of mass in motion, how much heat would you lose to convection off an uninsulated Al rod that's 54°F above ambient?
RobertSmalls is offline   Reply With Quote
Old 02-26-11, 10:40 AM   #5
mrd
Apprentice EcoRenovator
 
Join Date: Feb 2010
Location: Milford, DE
Posts: 106
Thanks: 5
Thanked 9 Times in 9 Posts
Default


The SQRTPI function did not do what I thought it did.

Attached Thumbnails
Click image for larger version

Name:	untitled.JPG
Views:	1630
Size:	61.3 KB
ID:	1293  
mrd is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:05 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design