Am I reading this current (amps) chart correctly?
Looking at Heating mode chart #2, it seems like, when the indoor set-point temp is 70F, and the outside temp is: 32F, the Sanyo uses 6.4 Amps 41F, the Sanyo uses 7.0 Amps 59F, the Sanyo uses 8.4 Amps And if it was 70F indoors and 70F outdoors, it would be using over 9 Amps?? Is it me? Or is something wrong with this picture?? |
02-27-11, 07:15 PM | #2 |
Journeyman EcoRenovator
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
|
I think you're reading that correctly. Heating capacity declines with temperature.
|
02-27-11, 11:10 PM | #3 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
But, when it's cold outdoors, I use about 10 or 12 kWh per day.
When it's warmer (like 59F), I only use 5 or 6 kWh per day. If it was 70F indoors and 70F outdoors, the dang thing wouldn't even turn on..(Not use 8.4 Amps). Just 60 watts for the crankcase.. I think the amps scale is upside down..?.. |
02-28-11, 04:51 PM | #4 |
Journeyman EcoRenovator
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
|
The thermostat regulates duty cycle to match the heating/cooling needs of the house.
|
03-01-11, 08:25 AM | #5 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
The house stays at about 70F 24/7.
Right now, it's 30F outdoors and the Sanyo is using about 480 watts. If it was 15 or 20F outdoors, it would be using more power, 600 to 800 watts. The colder it gets, the more power is needed to extract heat from the extra cold air.. The chart seems to show that colder means using less power! If it were true, then it would be cheaper to heat your home at when it was -12 deg outside! |
03-01-11, 05:35 PM | #6 |
Journeyman EcoRenovator
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
|
So your thermostat scales back power draw instead of duty cycle. The effect is the same. Although the above plot shows how much power the heat pump is capable of drawing at any given temperature, that doesn't mean it will do so 24/7.
|
03-01-11, 06:35 PM | #7 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
Like any other heating system, when it's real cold outdoors, it uses more power to keep the house warm.
Plus, I can see the power used instantaneously. (and by the day, week and month). |
03-01-11, 07:50 PM | #8 |
Apprentice EcoRenovator
Join Date: Feb 2010
Location: Milford, DE
Posts: 106
Thanks: 5
Thanked 9 Times in 9 Posts
|
The chart doesn't seem to make sense. Sure, the maximum capacity of the system declines as the outdoor temperature drops. But, does the power draw of the compressor also drop? I fail to see why that would be so.
The compressor may have a limited maximum RPM, and when it is colder outside, the maximum refrigerant temperature may be colder. Perhaps it takes less power to compress colder refrigerant, and the power draw is limited because the compressor RPM is limited due to friction at internal seals or some other mechanical limit? This is the only practical reasoning I can find. However, I would find it surprising that the max refrigerant temperature is so much lower that it could affect power draw so drastically. |
03-01-11, 09:42 PM | #9 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
It sucks warm air out of the cold
and when it's really cold, it starts sucking the money out of my wallet..
I've seen the power increase and can heard the fan cranking up to max speed on really cold nights. When I saw the mistake in chart (2), I started worrying about Chart (1).. I need that chart to be accurate, because I want to measure the R410A pressure. It shows the pressure going up as the outdoor temp goes up.. Cold air is going to lower the pressure.. Sounds logical.?. |
03-02-11, 06:26 AM | #10 |
Journeyman EcoRenovator
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
|
Capacity declines faster than CoP as outdoor temperature falls. I assume this takes the form of lower RPM, lower pressure, and less current draw at lower temperatures.
A plot of total daily power consumption versus time would require them to know what sort of house you've installed it in, the orientation of your windows and the sun, etc. Do you think that's the sort of plot Sanyo has supplied you with here? |
|
|