A simple check valve has a metal disk. The weight of that disk is probably enough to stop convection flow. I suggest just adding a check valve after the pump. I would not use a check valve with a spring because residential hydronic circulating pumps are low head pumps - they create very low pressure. The pressure needed to push the spring open will reduce flow, and could completely stop the flow.

And you are correct. A stopped centrifugal pump will not stop water flow. The water flows right through the pump.