simenad, wow, really nice temps for that deep. If I had that I would total have a solar powered well pump going though a radiator or two and feeding back into another well.

Jeff, yes I was hoping to be able to speed it up, not slow it down. I did a lot of digging and came to the same conclusion. SO I stole a fan from the disappointing dehumidifier and wired it on low. Then I had to add more charge because my super heat went crazy.
New data
Suction 91 psi
Discharge 241 psi
Superheat 9-12
Subcooling 10-12
Amp draw 4.06 @ 117 volts.

This morning I had it run for 4.5 hours (with the old fan and charge) and it sucked out slightly over a gallon. But now I can FEEL the cold air, plus it is going drip.drip.drip.drip, instead of drip..drip...drip..drip, and sometimes it even goes dripdripdripdrip.drip. LOVE it. It is 95F outside, and i've only used 24.8 kwh today. AND today is wash day. Compared to 72 kwh a year ago!! And I haven't even put in the geothermal unit yet.