Quote:
Originally Posted by oil pan 4 View Post
The spot welder says it can take a 50% duty cycle.
I think if I tried to run it at a real 50% duty cycle it would smoke the transformer.
Realistically I think it's good for more like a 20% to 30% duty cycle depending on ambient temperature.
The factory cord appears to be metric equivalent of about 16 gauge.
I can power factor correct it and drop a few amps.
So far fixed 6-20 circuits are 12 gauge wire and 20 amp breaker. Equipment 6-20 receptacles have 10 gauge dryer cord feeding the plasma cutter then it splits at the main buss inside the machine with 12 gauge wires that are maybe 1 foot long going to the 6-20 receptacle.
6-20 receptacle is 240 VAC single phase 20 amp . Fine to run # 12 copper , but should be wired to a 2 pole 20 anp CB .