Old 03-09-17, 04:03 PM   #4
Ormston
Apprentice EcoRenovator
 
Join Date: Mar 2013
Location: UK
Posts: 131
Thanks: 13
Thanked 35 Times in 32 Posts
Default

UK regs (not that they apply) state 50mm, this is purely from a safety point of view and not interference.

The idea is that if the insulation on the Band 1 circuit (ethernet in your case) is not rated for Band 2 (mains voltage) then any damage to the mains cable could also bridge the undamaged Band 1 cables insulation and provide your router/pc with mains voltage.

From an interference point of view, ethernet is fairly tolerant. If possible 250-300mm should be adequate, failing that ftp (foil screened cable) grounded at 1 end or steel conduit again grounded at 1 end only will prevent any issues.

Also remember that to get the best possible throughput, the cat 6 should have no kinks or severe bends as it will be operating at rf frequencies and is more of a wave guide than a conductor.

Steve