View Single Post
Old 02-18-16, 06:31 AM   #195
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by MEMPHIS91 View Post
Had my thinking cap back on for this project.

Considering my local weather https://weatherspark.com/averages/31...-United-States
I have several days that are going to be warmer than the pond while I am heating. Example, today it got to 56F, so my unit would be running more efficient running air source than it would be pond source (42F) today. This isn't uncommon either.
SO should I tie in the air source coils and have it on a solenoid on days like, so it can use the warmer air? It would be a design nightmare so the next question would be is it worth it? lol
You can try running an air-sourced zone. All you do is plumb in the air hx at the discharge line and make sure the suction side merges alittle distance past the sensing bulb for the water loop. Control flow with an external equalized txv. When the water is warmer than the air, the txv will sense the increased pressure and close. When the air is warmer, the bulb will sense the temperature rise and open the valve.

Mejunkhound did this with his ground source system. I believe he also has some kind of low ambient cutout control rigged in somehow. To control whether or not the fan blows air? I can't remember. It's in this forum, though.
jeff5may is offline   Reply With Quote