Sorry I did not explain the digital readings. They are for superheat and subcooling. So suction temp is the lower reading, and the temp 6" from the txv is the higher temp.

Yes this txv is non adjustable.

Yes that is why I charged up more in the first picture with a subcooling of around 5-7F because low subcooling tells me I have a staved condenser. But the R1270 bar to psi through me off.
So far the condenser has taken everything I have thrown at it. Every 15 minutes an air pump comes on for 2 minutes and stirs the water around the coil nicely.