Hi,
I'm not sure how this works, you're using the PV modules to do what? Also a 1k inverter at 120 volts will only put out a little over 8 amps at 220, only 4 amps. Did you say you want to run welders with this? It won't do it, perhaps I'm missing something?

Rob

ps:

A 40 AH battery really only has 20 AH's. You don't want to drive a battery to less than 50% charge because battery life is rated in charge cycles and the deeper you discharge the fewer cycles you have. Even 50% is less than I'd ever want to discharge even a good deep cycle battery like a Rolls or a Trojan.