The pressure held overnight. I have been trying to vacuum down the system. New oil in the pump a shut off valve close to the unit. It never got below 500 Microns I checked the vacuum pump with just one hose and the gauge it went 200 Microns no problem. I checked the two hoses and the valve. The valve will not let it get below 400 Microns so I have a bad valve.
I tried the manifold gauge same it would not go below 400 Microns. So I just went from pump to gauge then to outside unit. It was a 300 Microns @4:20 and slowly decreeing 225 Microns @5:10. I guess the plan is to keep it below 200 Microns for a hour then release some 410 from the liquid valve when the pump sound changes disconnect it @the gas valve.

Then let a little more 410 out check for leaks if none release both valves.
I just ordered three 410 ball valves for the next install.