Yeah, fooled me. I would not have expected an older non-inverter unit to have serial.
I guess the newer stuff is just a copy of the old stuff..
Pin #1 is a bi-directional control line. So, you not only send commands outdoors, you read back status data too.
Seems like it would be simpler to wire your control pair across the test button.. Brute Force Control.
Outdoor
• Once push : Ignore Communication error.
• Twice push : Comp. ON, / Outdoor Fan ON / Reversing Valve Coil ON(only Heating Model) / Crank Case heater Coil ON(only Heating Model)
• 3 Times push : Comp. ON, Outdoor Fan ON / Reversing Valve Coil OFF(only Heating Model) / Crank Case Heater Coil OFF(only Heating Model)
• 4 Times push : Same
• 5 Times push : Error LED(Red) ON
• 6 Times push : Comp OFF, Outdoor FAN OFF
• 7 Times push : Reset
That might get you the basic operations you need. If it will stay running in the test mode.. (No time-out).
And, you will likely have all protection/defrost functions too..