I just ran a little test.
There is 1 minute 15 seconds of burner run time prior to the blower starting.
Blower Time, Temp rise, percentage of max temp rise, %*57000BTUhr
1 minute, 25 degrees, 33%, 18810
2 minutes, 40 degrees, 53%, 30210
3 minutes, 50 degrees, 67%, 38190
4 minutes, 60 degrees, 80%, 45600
5 minutes, 65 degrees, 87%, 49590
6 minutes, 70 degrees, 93%, 53010
9 minutes, 75 degrees, 100%, 57000 (or about 10 minutes of the gas burner running which is actually 12 minutes of call for heat since my furnace takes 2 minutes from the call for heat until the burner kicks on)
After shutting down the furnace
1 minute, 50 degrees, 67%, 38190
2 minutes, 35 degrees, 47%, 26790
I'm not sure how to calculate all of this but if I add all of the figures together and average them I suppose I'll get somewhat close. It seems that I'm getting 67.75% of the steady state heat output in the first 10 minutes of operation including the cooldown period or about 38618 of the 57000. Which is 51.49% of the 75000 input rate. Seems a little hideous to me. What's worse is the previous owners had a thermostat that only had the gas valve running for 5 minutes which looks like an even worse proposition considering the temperature through the registers is still rising. If I take the 10 minutes and change it to 20 minutes, things look better at 91% of the heat output versus 67.75% of the 10 minute figure and 94% if we make a 30 minute run.
Granted, this math is rough but I think it illustrates the point.
|