Quote:
Originally Posted by Marc_NL View Post
... it is a Danfoss DHP-C 6 which is a 6kW heat pump including 180L DHW tank (with electrical back-up heating up to 9kW) and including the heat exchanger for 'natural' cooling (without the heat pump active). It is rated at a COP of slightly above 4 (including pumps) for 0C water in and 35C water out (which is more than enough for the underfloor heating). Surely the COP for DHW will be much lower...
Sounds like quite the find, and at a price that you like!

I understand BTUs better than kW... so, 6kW works out to 20472 BTU, which will certainly be ample, especially if you are going with Passive House standards as your guide.

How many square meters is your home going to be? On one floor or multiple levels?

Best,

-AC