Might of figured out how to identify the Btu gains

The Btu gain conversion calls for the Fan CFM x 1.1 x difference in inlet vs outlet temperatures.
Using the hot side temps to measure gains seems to work

Room temp of 75f minus by the Hot side of 115f = 40*f gain

Fan 240cfm x 1.1 =264 x gain of 40f =10,560 Btu

The unit is rated to make 11,000 btu

If the hot side in/out numbers are used as the the inlet /outlet temp the math works.

Using the cold intake temp of 44f vs the 115f hot outlet with the above math shows a 19,800 Btu gain. I doubt that right.

The only numbers left are the cold sides in/out of 44*f in / 14 out with a 240CFM fan that math shows a 7920 Btu gain which is closer to the hot sides result