It can "export" on the input but that would be "net metering" you can set it to export by setting the "sell" amps. so if you know the load amps you can do that. But, if that load drops it will export to the grid. On the Plus side it is 1741 certified so if the grid goes down you will not backfeed.

As to the net Zero setpoint. On the most current firmware version I can set the battery DOD from 0 to 100% so its not a issue. You have full range of when the inverter goes from Net-zero to grid use.

Maybe I don't understand what your really wanting to achieve in regards to powering loads on the input side.