Default

Awesome info thanks!

So a larger compressor to push my unit out of its comfort zone is a good thing, so I'll still be looking for one close to a ton.

I ordered the TXV so we shall see how that goes as well.

I believe you are saying my discharge psi is to high? Or should I push a higher psi? Little confused on that, I know you said with higher charge more liquid gets stored in the condenser but is that related to psi too?

Or could I blend some 410a into the mix to bring down the suction temp some?

I will install a high and low pressure cut off as well just to make things safer and save a compressor.