Quote:
Originally Posted by pedro View Post
Here is live data on my geo
Link now included. I monitor entering water temp, leaving water temp and GPM. I also monitor geo power and well pump power. (got a new monitoring unit as I found the current one is a little off due to the power factor). I also monitor supply and return temps. I then calculate the heat of absorption for the water flow and the overall output of the Geo. From all that I also calculate COP which is a little low because the geo power reads a little higher than what it is. I found on avg going from 3.25 - 3.5 gpm to 4.75 to 5.25 gpm raised COP about .25 or so plus I was putting about 4000 BTU/h more but my pump when from 33% on to 49% on.


You can see live data on my unit here: https://dweet.io/follow/yumyum
pedro is offline   Reply With Quote