Quote:
Originally Posted by charlesfl View Post
Heat Capacity: Water Furnace assumes that in addition to the heat extracted from the source water loop, the electrical energy consumed by the heat pump is also converted into heat and fed into the load fluid

Geothermal Water Heating Efficiency study (Second cut).

I found this explanation on the our cool house web site.

charlesfl
When I was trained to fast-fill SCUBA tanks, I was told to always put the tank
in a big bucket of water, to keep the steel tank from over-heating.
I asked my boss, "is the steel expanding and getting hot"?
He said, nope, it's the atoms inside the tank being forced together so hard.
They are rubbing against each other, producing friction heating.

Since we used large air tanks to fill the SCUBA tanks, with the compressor off,
it's electric motor heat wasn't contributing to the hot air in the SCUBA tank.


I can see how the motor's heating is going to put some BTUhs into the R410A,
but the amount seems too small to account for the difference in pumped BTUs (heat vs cool).

1 watt hour of motor heat equals 3.412 BTUh.

5,000 BTUh of extra heating from the motor heat, means it would be
producing 1.465 kWh in heat losses.. That would blister the paint..
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..