Assuming a 250w panel and the slightly older M215 inverters, there is a max of .91A x 60 panels = 54.6A x 1.25 (safety) = 68.25A.
So you would need a #4 wire as #6 is only approved up to 60A. Note that you are on the low side of the capacity for a #4 (at a minimum) so without doing much more calculation, I suspect you would be quite good for voltage drop too. #2 is more typical for a 100A service (if you use a 90C wire).