Mark Steele 12-08-12 05:55 PM

Heat pump water heater modification.
 
Hi I have a GE geothermal heat pump water heater. I'm hooking up a water / freon heat exchanger to it. I'll be installing it in between the expansion valve and the evaporator. I noticed that the freon feeds into the evaporator at the bottom and exits out the top. Does anybody know if it matters if I mount the heat exchanger above or below the evaporator inlet line , and if it matters if the freon is fed into the top or bottom of the heat exchanger?
Thanks

Mikesolar 12-08-12 06:50 PM

Liquid should enter at the bottom as it becomes a vapour and you want to have a high quality vapour exiting without any liquid drops. I think it best to have the evap equal to or higher than comp but it may not be that critical.

Daox 12-30-12 01:33 PM

Any updates on this project Mark? Did it work out?