theoldwizard1 11-01-14 09:23 AM

Newbie question about "other" components
 
While typically not shown in heat pump functional diagrams, frequently heat pump systems have "other" components such as
  • receiver
  • dryer
  • accumulator
  1. Where do these component fit in the overall heat pump system ?
  2. What is the function of each ?
  3. Why do some designs have them and others do not ?
  4. Any other components I have missed ?

jeff5may 11-02-14 05:03 PM

Most of these parts go in larger and variable capacity systems. With larger systems, these are used to head problems off at the pass.

Filter-dryers are (99% of the time) installed in the liquid line to keep the refrigerant and oil clean, as well as scavenge any stray moisture that may exist in the system. Any time the refrigerant system is opened, the filter is changed as cheap insurance against big deadly problems.

Liquid Receivers and suction accumulators are vessels that buffer what is downstream from them from what they shouldn't be fed. Receivers feed expansion valves liquid, accumulators feed compressors gas. These vessels also act as reservoirs for excess refrigerant in the system. With heat pumps, the reverse cycling sometimes causes a full condenser to "burp" its charge into the low side of the system as it depressurizes. A suction accumulator catches this "spew" before it can reach the compressor inlet.

Many larger systems have multiple evaporators and condensers. When these "extra" heat exchangers come online or offline, the required refrigerant amount changes, so the "extra" refrigerant is stored in or drawn from these vessels.

NiHaoMike 11-02-14 05:41 PM

And in the smaller systems we typically see here, the filter drier often doubles as a liquid line receiver. For that to work as expected, it must be installed such that the outlet is at the bottom.

jeff5may 11-02-14 06:30 PM

Yup, yup, and I've got a pic of one:

http://i1326.photobucket.com/albums/...psaa424bee.jpg

don't ask me why, but the manufacturer put this one in upside down. If you're going to hack a small unit, this "charge-o-valve" is the easiest way to tap into the liquid line. Parker No.620 or equivalent clone. This one doesn't have an access valve where it should, since valves cost more than brazing rod.