Santa Fe Classic Dehumidifier
1 Attachment(s)
This looks like the perfect unit for my basement!
Buy Santa Fe Classic Basement & Whole House Dehumidifier (4029700) | Thermastor 4029700 Capacity @ AHAM: 110 Pints/Day Capacity @ Saturation: 180 Pints/Day Amp Draw: 6.4 Amps CFM: 275 CFM Operating Temp. Range: 56° - 95°F Wow! Listed at $1,671.00 Got it off craigslist for $100 See: http://ecorenovator.org/forum/sale-t...list-used.html It seems to be working Okay. In ideal conditions, it pumped a cup of water in about 35 minutes. After I install some filters, I'll give it a good test run.. It does use about 6.4 Amps at 120vac.. http://ecorenovator.org/forum/attach...1&d=1468878596 |
Great deal.
|
Gut shots? Or did it already get installed somewhere?
|
1 Attachment(s)
I think it's a 6 or 7 years old. Recently replaced. No explanation of why..
But, when I did a short test the day of delivery, it was idea weather for a test. Raining & 80F. in an open garage. Looking at the amount of water that came out. I estimate 1/2 quart per hour. (or less). Spec says under idea conditions, 2 quarts per hour. On some of the reviews I've seen, there were owners saying that refrigerant slowly leaked out. (4 or 5 years) I hope that's all that's wrong with this one.Hope it just needs a shot of R410A.. Planning to test some more when I get some air filters. Noticed the compressor got really hot. Wondering what the normal operating temperature is.?. |
1 Attachment(s)
The maintenance port is out on a thin tube..
I can see how it might get broke off when removing the cap.. |
Pressure test?
1 Attachment(s)
If I put a gauge on the low pressure port while the unit is running, I should see about 240 PSI?
Or, is that the Max pressure? On a mini-split, it seems like 130-140 PSI is common.. http://ecorenovator.org/forum/attach...1&d=1469311501 |
Kinda working..
1 Attachment(s)
I'm not so sure.. I found a user that's had a lot of problems with this model..
Sante Fe Classic Quality Issues He's included five links to YouTube videos in his posts.. Mine seems to be working poorly. Only getting about a quart during a 1 hour run.. Temp 70F with RH between 60 & 70 percent. I'm wondering if a Superheat test could tell me anything.. First, I'll have to find out what the 'standard' Superheat temperature is for this model. At 70F & 70%RH.. ~~~~ After a 1/2 hour warm up, I did a little testing of the input air vs the output air. Input air was 62%RH @ 73deg Output was 38%RH @ 82deg A change of 24%RH & 9 deg. |
Maybe I'm lucky or something, but we bought a Thermastor Santa Fe Classic dehumidifier in 2003. We put it in the living room to use as a whole house dehumidifier in summer. It's been working perfectly ever since.
The house temperature is typically 75 to 80 deg F, humidity 45 to 50%. The house is well insulated, so we rarely use the AC. Also, the AC does not do a good job of removing moisture. My wife likes it dry, sometimes the humidity gets down to 40%. |
Wow! That sounds like money well spent.
Is it a R22 or R401a version? I'm also very interested in the temperature of the input air, vs the output air. I think it might be a quick way to determine the correct refrigerant load. If I can get this one working to spec, it would be fantastic for our musky basement.. |
The nameplate says R22. It's running right now. The room temperature is 76 deg F, 53% RH, outlet temperature is 100 deg F. The outlet temperature reading may be a little low, it's a cheap little thermometer laying on the floor.
|
All times are GMT -5. The time now is 06:57 PM. |