Old 06-07-16, 11:51 AM   #11
pinballlooking
Super Moderator
 
pinballlooking's Avatar
 
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
Default

Quote:
Originally Posted by LJKeenan View Post
your getting frost on the small line?
Yes it is completely white with frost.
I turned it back off for now.

I did some internet research and this seems like a common issue for a mini split if you have a low Freon charge.
It looks like I should just keep it off until my Freon comes. My Freon was shipped today. My system takes 45.9 oz. Freon.

__________________
Current project Aquaponics system , Passive Solar Greenhouse build

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Solar Install 12.5 Kwh-
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Mini Split installs -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

EV Chevy Volt -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Last edited by pinballlooking; 06-07-16 at 01:10 PM..
pinballlooking is offline   Reply With Quote
Old 06-07-16, 02:36 PM   #12
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

http://ecorenovator.org/forum/geothe...project-3.html

"Got some chill testing done. I found the 4-Way valve default in T-Run mode is heating.
After seeing some high power use in heating, I decided to disconnect the 4-way valve,
and do my testing today in chill-out mode.
Note: The 4-Way valve is marked 230vac."



Maybe try disconnecting the 4-way valve.. Just to see if it has voltage on the connector.. If it has voltage, try leaving it disconnected and check the cooling.?.
If there is no voltage, change to heat mode to see if the voltage is there.?.
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 06-08-16, 04:07 PM   #13
pinballlooking
Super Moderator
 
pinballlooking's Avatar
 
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
Default

I have a good flare tool, Freon and a leak detector coming.

Luckily my LG units are working very well so I have a directional fan blowing the cool air down the hall into my room.

Attached Thumbnails
Click image for larger version

Name:	Fan.JPG
Views:	779
Size:	35.0 KB
ID:	7000  
__________________
Current project Aquaponics system , Passive Solar Greenhouse build

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Solar Install 12.5 Kwh-
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Mini Split installs -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

EV Chevy Volt -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
pinballlooking is offline   Reply With Quote
Old 06-14-16, 12:13 PM   #14
pinballlooking
Super Moderator
 
pinballlooking's Avatar
 
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
Default

I cut off the bad flare and made a good flare connection. I pressure tested my system overnight with 150 psi. nitrogen. No leaks.
The approach I took was to vacuum it down with the 2 way and 3 way valves open to about 600 microns.

For about one hour. Then I closed the 2 way and 3 way valves and vacuum it down to 400 microns.
(Was this the right approach?)

I purged the Freon hose opened 2 way and 3 way valves and charged it by weight.


I rechecked the flare fittings for leaks all good.
It is now putting out very cold air again!!!


We are having a heat wave 95 yesterday 95 today. It is so welcome to be cooling again.


Day two.
I was so nice to wake up in a cool room with lower humidity.


I ended up with this flaring tool.
Mastercool 70058 Eccentric Flaring Tool Kit
It takes the guess work out of how tight to make the tool.



Day three and AC still doing really well. It is 97 degrees F today.
The 9,000 BTU AC is keeping up really well. I was starting to think it was not big enough for this room. But it must just been getting low on Freon because now it is keeping fine.
Attached Thumbnails
Click image for larger version

Name:	20160614_125222.jpg
Views:	759
Size:	27.0 KB
ID:	7011   Click image for larger version

Name:	ValvesJPG.JPG
Views:	787
Size:	47.6 KB
ID:	7012  
__________________
Current project Aquaponics system , Passive Solar Greenhouse build

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Solar Install 12.5 Kwh-
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Mini Split installs -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

EV Chevy Volt -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Last edited by pinballlooking; 06-16-16 at 04:42 PM..
pinballlooking is offline   Reply With Quote
Old 06-21-16, 09:21 PM   #15
pinballlooking
Super Moderator
 
pinballlooking's Avatar
 
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
Default

I was 98 degrees today and one week since the mini split repair. I am happy to say it kept up today nice and cool.
__________________
Current project Aquaponics system , Passive Solar Greenhouse build

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Solar Install 12.5 Kwh-
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Mini Split installs -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

EV Chevy Volt -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
pinballlooking is offline   Reply With Quote
Old 06-21-16, 10:39 PM   #16
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Awesome! I would imagine this is a much better solution than spending $600 or more for "the guy" to come to you and do it.
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
pinballlooking (06-21-16)
Old 06-21-16, 10:50 PM   #17
pinballlooking
Super Moderator
 
pinballlooking's Avatar
 
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
Default

Thanks!
So much better to be in control of the fix. I learn a little more each time.
It peeks my interest to learn even more.
I have over 20 pounds of 410A left over for future issues/projects.
__________________
Current project Aquaponics system , Passive Solar Greenhouse build

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Solar Install 12.5 Kwh-
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Mini Split installs -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

EV Chevy Volt -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
pinballlooking is offline   Reply With Quote
Old 06-22-16, 08:31 AM   #18
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

You better hope you don't get a power spike into your main control board!
Invest in protection for your 230vac source.. (Of course mine didn't work)..

I was just reading a couple of depressing reviews at HomeDepot..
One buyer couldn't get an installer.. The other buyer may have gotten a bad install..
Seems like most nothing is ever 'easy' in this life.
GREE Multi-21 Zone 18,000 BTU 1.5 Ton Ductless Mini Split Air Conditioner with Heat, Inverter, Remote - 208-230-Volt/60Hz-MULTI18HP200 - The Home Depot
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 06-22-16, 08:59 AM   #19
pinballlooking
Super Moderator
 
pinballlooking's Avatar
 
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
Default

I have lighting suppressors on main load center and the panel where the solar comes in. For whatever that is worth.

When I bought my first Mini split I got a quote from a HVAC guy that has done work for me in the past.
He wanted to buy the equipment because they make money on the hardware. He said since I did not buy the hardware from him he would have to charge more for the install. The install was going to cost just a little more than the mini split did. He is installing Gree mini splits and has had good luck with them.

It also seems that there is not a lot of experience with mini splits yet.

That did not work for me so I took all your advice and bought the equipment and did it myself.
I am glad I did.
I think if you buy the more reasonable priced models you should buy their top of their line equipment.
Most of the time you will have better luck with it. I know this is not true 100% of the time but it has worked pretty well so far.
__________________
Current project Aquaponics system , Passive Solar Greenhouse build

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Solar Install 12.5 Kwh-
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Mini Split installs -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

EV Chevy Volt -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
pinballlooking is offline   Reply With Quote
Old 06-22-16, 10:59 PM   #20
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Another good thing about buying premier products is the support you get. If something does go wrong, most manufacturers stock more parts for the premier products than the "plain" products. They also offer a longer warranty and more comprehensive tech support in many cases. If you are doing a self-install, it makes sense to spend a little of what you are saving on an upgrade.

jeff5may is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 09:55 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design