Quote:
Originally Posted by abogart View Post
I like the dehumidifier idea (posted near the beginning of this thread). What about placing the evaporator coil in the cold/stale air going out, and the condenser in the cold/fresh air coming in? Basically putting a small HP on the outside air portion of the HRV system. Dehumidifiers don't use much electricity. It seems to me like that would greatly improve energy recovery. The HP would not only be using the heat energy from the incoming air from outside, but also the heat that the HRV doesn't recover. To me, it seems like this system would produce much more heat than an air-air HP located outside. Ductwork could be made to reverse the system during the warmer months.

EDIT: oops, got my condensers and evaporators confused
This is an excellent idea, and a small dehumidifier would supply all the required parts.

-AC_Hacker

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 01-22-12, 06:24 PM   #202
Beenthere
Lurking Renovator
 
Join Date: Jan 2012
Location: Dayton, Ohio
Posts: 1
Thanks: 0
Thanked 0 Times in 0 Posts
Default

AC Hacker, Thank you for all your posts here as well as Homemade Heat Pump Manifesto. I have read all of them with great interest. You and all the others have given me so much information. I too will soon start hacking!

Last edited by Beenthere; 01-22-12 at 06:29 PM..
Beenthere is offline   Reply With Quote
Old 01-23-12, 11:08 AM   #203
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by Beenthere View Post
AC Hacker, Thank you for all your posts here as well as Homemade Heat Pump Manifesto. I have read all of them with great interest. You and all the others have given me so much information. I too will soon start hacking!
Welcome!

I don't know your background, but I usually advise folks to start with small projects and gradually move to more ambitious ones.

Do you have a project in mind already?

-AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 01-24-12, 05:17 PM   #204
pladijs
Lurking Renovator
 
Join Date: Jan 2012
Location: belgium
Posts: 13
Thanks: 2
Thanked 2 Times in 2 Posts
Default small plate heat exchanger with aluminium foil

I have been following this thread for a while, and got appetite to start on something myself.

I live in a small 60m2 apartment in an old renovated building. Three rooms in a row, livingroom-kitchencombo, and the last room is my bedroom, with a bathroom semi-attached (no door between them). I renovated this apartment myself, not hindered by much background knowledge, and overlooked a major thermal bridge in my tiled bathroom floor, aggravated by the fact that my neighbor downstairs decided not to use that space at all and does not heat it (he has a larger apartment). Result: lots of condensation on the floor, even when it's just chilly outside (say 6C).

Another source of humidity is cooking: it would have been quite difficult to install a true extractor hood given the setup here, so I'm stuck with a recirculating system. You guessed; there's a lot of humidity, cold spots, I can start to smell mold developing. A seriously bad situation.

A simple extractor fan in my bedroom/bathroom would help a lot, but I’d actually like it to run continuously to improve the air quality throughout the entire place. I’ve been planning to install a HRV unit, and given that its purpose would also be to extract humidity, I’m excluding systems with humidity recovery. Given the price-tag of commercial systems, and an uncontrollable desire to mess around with stuff, I was thinking of getting started on my own HRV.

To cut it short: after quite a bit of reading around, remembering what I liked and ignoring good advice, I thought I’d buy a piece of 4mm or 6mm thick double-sided polycarbonate board, and cut out the individual channels with a cutter (resulting in many thin long pieces of hollow plastic). Then, make flimsily thin empty frames out of this, about 90cmX44cm in size, and then stretch aluminium foil over them, make a stack of them, say 40 pieces, and take an approach somewhat like in the “make” article which was posted above. I would use some silent 120mm fans. I’ve taken up soldering, so I’m looking forward make this run slowly, and somewhat faster when the relative humidity increases.

Questions I have are: does this make any sense whatsoever? Would the fans be able to push the air through (tell me there’s not enough information here to know). Any idea on this surely being so inefficient it cannot be worth it? A specific question I have is: would it make sense to force the flow between the plates to follow an S pattern, using baffles somewhat like in a shell-and-tube heat exchanger. Would such baffles just decrease the capacity? Would they help creating a turbulent flow? In that respect: would it help to try creating a more rugged surface of aluminium?

Lots of questions, not too much structure, long post. Really sorry about that, but any comment is greatly appreciated!
pladijs is offline   Reply With Quote
Old 01-25-12, 01:19 AM   #205
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by pladijs View Post
...after quite a bit of reading around, remembering what I liked and ignoring good advice, I thought I’d buy a piece of 4mm or 6mm thick double-sided polycarbonate board, and cut out the individual channels with a cutter (resulting in many thin long pieces of hollow plastic). Then, make flimsily thin empty frames out of this, about 90cmX44cm in size, and then stretch aluminium foil over them, make a stack of them, say 40 pieces, and take an approach somewhat like in the “make” article which was posted above. I would use some silent 120mm fans. I’ve taken up soldering, so I’m looking forward make this run slowly, and somewhat faster when the relative humidity increases.

Questions I have are: does this make any sense whatsoever? Would the fans be able to push the air through (tell me there’s not enough information here to know). Any idea on this surely being so inefficient it cannot be worth it? A specific question I have is: would it make sense to force the flow between the plates to follow an S pattern, using baffles somewhat like in a shell-and-tube heat exchanger. Would such baffles just decrease the capacity? Would they help creating a turbulent flow? In that respect: would it help to try creating a more rugged surface of aluminium?
> ...there’s not enough information...

I think your idea will work, and it's not going to be terribly expensive to try it out.

I don't quite get the "S" curve thing... Why not just go with a longer channel?

But the most important thing is to try it out, do some tests...

You got it right the first time when you said that you were, "not hindered by much background knowledge."

I think that is the perfect state of mind with which you should proceed!

Please take photographs of your project, we'll all be very interested to see what you come up with.

Regards,

-AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 01-26-12, 08:46 PM   #206
philb
Apprentice EcoRenovator
 
Join Date: Nov 2010
Location: Oklahoma City
Posts: 155
Thanks: 58
Thanked 17 Times in 14 Posts
Default

Here's an addition from Grainger. Energy Recovery Ventilators
http://www.grainger.com/Grainger/ene...rch&sst=subset

Last edited by philb; 01-26-12 at 08:54 PM.. Reason: url posting issues
philb is offline   Reply With Quote
Old 01-27-12, 03:20 AM   #207
pladijs
Lurking Renovator
 
Join Date: Jan 2012
Location: belgium
Posts: 13
Thanks: 2
Thanked 2 Times in 2 Posts
Default

Thanks for the feedback. I meant the approach of David L. Meinert, btw, not the `make' article.

do you people know these HRV's, might be inspiring...

http://www.homeventilation.co.uk/retroVent.php

comes at a 400 something GBP price tag, but I find it hard to believe the efficiency of 80-90% given the small surface.

This one, I'm extremely fond of, and there's lots of positive talk on it on German fora
http://www.oekoluefter.de/bilder.htm
http://www.oekoluefter.de/video.htm

It's by a tiny manufacturer. but it's a beautiful thing with magnetic bearings etc.

I had to mess up the urls, hope that works

Last edited by Piwoslaw; 01-30-12 at 02:09 PM.. Reason: Fixed URLs
pladijs is offline   Reply With Quote
Old 01-27-12, 11:23 AM   #208
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by pladijs View Post
...do you people know these HRV's, might be inspiring...
Yes, we did have some idea... There have been 21 pages of posts on this topic, and 208 posts in those pages.

But the most interesting part is the work that has actually taken place to try to build a useful heat exchange ventilator.

I took a look at the links you left on your previous post. The mechanisms that are being tried look like they may be a challenge to fabricate.


What are your ideas regarding your DIY project approach?

Have you made preliminary sketches yet?

What material will you use for the heat exchanger?

How will you deal with condensation?

-AC_Hacker
Attached Thumbnails
Click image for larger version

Name:	tube-HX.jpg
Views:	12412
Size:	18.3 KB
ID:	2041  
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 01-27-12 at 01:43 PM..
AC_Hacker is offline   Reply With Quote
Old 01-31-12, 04:20 AM   #209
roche
Lurking Renovator
 
Join Date: Dec 2010
Location: UK
Posts: 2
Thanks: 2
Thanked 0 Times in 0 Posts
Default

At the risk of being somewhat off topic, I have question: Given that running the house at a slightly lower pressure than the ambient atmospheric pressure is desirable, how will that affect say a log burning stove? Will it upset the flue balance unduly, causing it to become smokey?
roche is offline   Reply With Quote
Old 01-31-12, 10:19 AM   #210
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by roche View Post
At the risk of being somewhat off topic, I have question: Given that running the house at a slightly lower pressure than the ambient atmospheric pressure is desirable, how will that affect say a log burning stove? Will it upset the flue balance unduly, causing it to become smokey?
If it is desirable to run a slight negative pressure (is it?), and if you need to burn wood, then you most likely will need an air-tight stove with an external air supply.

All of the HRVs that I am aware of use balanced in-flow and out-flow fans to ensure zero pressurization.

Is the idea behind slight negative pressure an attempt to avoid moisture condensation in the walls?

-AC_Hacker

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
roche (01-31-12)
Reply


Tags
erv, heat recovery, hrv

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 02:54 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design