Old 06-12-09, 12:50 PM   #91 (permalink)
Apprentice EcoRenovator
 
jwxr7's Avatar
 
Join Date: Dec 2008
Location: mid michigan
Posts: 137
Default

Quote:
Originally Posted by b4u2 View Post
since I am building my own panels I can use whatever cables will work for me. the company I ordered my inverter thru went out of business & cancelled my order so I will have to order from somewhere else now. I have this 24v 100W panel & I can't do anything with it.
If you want your connections to be liquid tight at the inverter, you will need to either buy the special cables with one end that mates up to the inverter's DC connections or do what I did. I don't reccomend it, but you could also cut and strip the DC cables to connect to them. Problems with that are; they are quite short, that would be tough to keep liquid tight, and it's also hard to make reversable (to put it back to original). When I made my DC cable, I hard wired it in the solar panel's connection box. I didn't attempt to adapt to the bigger older style connectors used by my panels.


(Support EcoRenovator.org & get rid of these annoying ads!)      
 
jwxr7 is offline   Reply With Quote
Old 06-25-09, 01:20 PM   #92 (permalink)
Apprentice EcoRenovator
 
jwxr7's Avatar
 
Join Date: Dec 2008
Location: mid michigan
Posts: 137
Default

I need to come up with some sort of water cooling system for my array. These hot sunny days aren't producing nearly as much power as I expected. The panels are getting very hot and this lowers thier efficiency.
jwxr7 is offline   Reply With Quote
Old 06-25-09, 03:24 PM   #93 (permalink)
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 1,226
Default

Is there any commercially avaliable solution for this problem?
Daox is online now   Reply With Quote
Old 06-25-09, 03:41 PM   #94 (permalink)
X-Frenchy: very
 
groar's Avatar
 
Join Date: Sep 2008
Location: Toulouse, France
Posts: 153
Default

"Albedo" may be a part of the solution : find something clear that reflect the sun and cover the ground around the panels. Not only the panels will receive more indirect light, but the surrounding will be more cool and the panels less hot.

Hope I'll be able to take picture of what we installed lately to shade the office bay and the kitchen window. Not only they permit the office and the kitchen to not be hot, but the ground is more cool so the air at the base of the panels. I have only the feeling that it helps a little in my case, but I'm working on trying to find the way to show it without having to remove the shades.

Ventilation is also important. This is noticeably important for roof integration as I have and as it's privileged in France by better buying rates. Finding a more ventilated place could be a solution.

Water is certainly bad as it will make things to depose on the panels and will not remove so much heat. A way to remove more heat with water would be to mist it (make very small drops that instantaneously evaporate and absorb "a lot of" heat).

At least don't put them under some trees as I have seen it in a US TV series lately

Denis.
__________________
Earth absorbs 1.8 t CO2/head/yr, while a French generates 6.2 t CO2/yr
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
  • kg saved 06/08-08/09: 1816.9+382.9 (ecodriving / 1420mi not driven) = 2199.8
    To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
    (2.66 kg/l diesel)
  • kg saved by 3kWc photo-voltaic solar panels : 187 kg/yr
    To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
    (59.1 g/kWh)
Radioactive wastes saved by 3kWc photo-voltaic solar panels :
  • Long life (>100,000 years) : 2.85 g/yr (0.9 mg/kWh)
  • Short life (<300 years) : 31.7 g/yr (10.0 mg/kWh)
Based upon "official" French figures...
groar is offline   Reply With Quote
Old 06-26-09, 09:28 AM   #95 (permalink)
Apprentice EcoRenovator
 
jwxr7's Avatar
 
Join Date: Dec 2008
Location: mid michigan
Posts: 137
Default

Quote:
Is there any commercially avaliable solution for this problem?
I'm not sure, I haven't researched it too much yet. I will be looking though.

Thanks for the ideas Denis.
I don't think the area around the panels is getting too hot being vegitation mostly. Putting down white stone would probably help though, it would also keep the weeds down. I'm not sure I'm ready to commit to this location that much yet, with all the work putting stone down.

There are lots of minerals in our water, and I can imagine they would build up wherever it evaporates. That makes things difficult for misting or trickling. I suppose a network of tubes touching the back side of the panels with water flowing thru them could help, but isn't very practical or efficient. Maybe misting the back surface is an option, I just don't like the idea of putting moisture on all the wiring and inverter stuff back there.
I think a good first step would be to cut back the weeds around the area of the array for better ventilation. This needs done again soon anyway to eliminate shadows, but I'll clear even farther away than needed for that.

These long hot sunny days have only been giving me 1200 watt hours or so, and I know that isn't nearly as good as it should be doing .

Last edited by jwxr7; 06-26-09 at 09:35 AM..
jwxr7 is offline   Reply With Quote
Old 07-01-09, 08:17 AM   #96 (permalink)
Apprentice EcoRenovator
 
jwxr7's Avatar
 
Join Date: Dec 2008
Location: mid michigan
Posts: 137
Default

Here's the #s for June 2009;
total monthly production was around 27.42kwhrs.
averaging 914whrs per day.
Not as good as it should be considering the amount of sun we recieved.
I cut down the weeds around the array for 20 feet or so to help with ventilation on the 28th of june. Hopefully this will help cool the set-up some and get the #s up a bit.
jwxr7 is offline   Reply With Quote
Old 07-04-09, 06:40 PM   #97 (permalink)
X-Frenchy: very
 
groar's Avatar
 
Join Date: Sep 2008
Location: Toulouse, France
Posts: 153
Default

About your low numbers for June, which is the max instantaneous you could notice between 11 and 15 ?

Your output from the panels may be greater than the maximal input of your inverter. The inverter can then limit the input to the allowable max, or simply put itself in security and produce no output until the input is acceptable.

The efficiency of the inverter isn't a constant and isn't maximal at maximum input.

Denis.
__________________
Earth absorbs 1.8 t CO2/head/yr, while a French generates 6.2 t CO2/yr
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
  • kg saved 06/08-08/09: 1816.9+382.9 (ecodriving / 1420mi not driven) = 2199.8
    To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
    (2.66 kg/l diesel)
  • kg saved by 3kWc photo-voltaic solar panels : 187 kg/yr
    To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
    (59.1 g/kWh)
Radioactive wastes saved by 3kWc photo-voltaic solar panels :
  • Long life (>100,000 years) : 2.85 g/yr (0.9 mg/kWh)
  • Short life (<300 years) : 31.7 g/yr (10.0 mg/kWh)
Based upon "official" French figures...
groar is offline   Reply With Quote
Old 07-05-09, 03:54 PM   #98 (permalink)
Apprentice EcoRenovator
 
jwxr7's Avatar
 
Join Date: Dec 2008
Location: mid michigan
Posts: 137
Default

I'm not sure what you mean by
Quote:
which is the max instantaneous you could notice between 11 and 15 ?
? Is 11 and 15 the time, like between 11 am and 3 pm?

In the winter i have observed the panels maxing out the inverter. It would hit 204 watts and not climb anymore. On several occasions during hot sunny days I checked the inverter output, but it was only about 120 watts. I would have expected it to be maxed out under those peak solar conditions. I remember one day feeling the panels with my hand. They were extremely hot. Aren't the polycrystalline type like mine effected more by temperatue? I also felt the inverter and it wasn't too bad.

The suns path thru the sky is actually quite far north in the morning and evening too. Making me want to angle my array that way slightly, or at least go totally flat. They seem to recommend this for lower lattitudes, but not mine.
jwxr7 is offline   Reply With Quote
Old 07-05-09, 05:02 PM   #99 (permalink)
Apprentice EcoRenovator
 
jwxr7's Avatar
 
Join Date: Dec 2008
Location: mid michigan
Posts: 137
Default

I just checked my inverter output at 5pm. It said zero watts. It's nice and sunny, but later in the day, not so late as to cut off output. It shows that the array logged around 640 watt hours for the day (not too impressive). I went out and the inverter was cool to the touch, panels were quite warm. I opened up the DC junction box and the array voltage was around 46 volts. I checked each panel and they were between 11.5 and 11.75 volts. The middle ones were lower than the outer ones (heat related?). I thought about experimenting with some water cooling but it's late enough that the sun may not be at a good angle for the test. Maybe tomorrow I'll try something during peak solar conditions. I hope the glass can take the rapid temp change (I'm sure they are tempered). I also suspect the array angle some, but if cooling brings the voltage up dramatically, I'll drop that suspect.

Last edited by jwxr7; 07-05-09 at 08:48 PM..
jwxr7 is offline   Reply With Quote
Old 07-05-09, 06:10 PM   #100 (permalink)
Apprentice EcoRenovator
 
jwxr7's Avatar
 
Join Date: Dec 2008
Location: mid michigan
Posts: 137
Default

I checked output again at 7pm and it was making 45 watts or so . Array angle isn't the problem. Went out and felt the panels, they were fairly cool now, the inverter felt the same as earlier. Got under the array and checked the array voltage, I think it was around 38 volts . Now that made me go back and check the input parameters to my inverter. It looks like the info I printed off gives the minimum DC input voltage as 44 volts. So what the heck is going on? I might be having some kind of inverter issue. It should have been producing earlier when it was in the 46 volt range, especially if it was working below 40 volts just a while ago. An EMU would be nice to have right now. I'll have to do some connection checking.
jwxr7 is offline   Reply With Quote
Reply

Tags
electric, solar

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Dorgard
Be assured of your business' safety with battery operated and self-contained Dorgard.
Property Prices
Check out property prices on your street with Zoopla!
Replacement Windows
Look at windows on everest.co.uk and choose the style and material you prefer then add as many finishing touches as you wish.
Divan Bed
Click here to order the divan bed you are looking for.

All times are GMT -5. The time now is 03:27 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.3.2
Ad Management by RedTyger
Inactive Reminders By Icora Web Design