Old 12-24-09, 10:13 PM   #21 (permalink)
New Guy
 
Join Date: Dec 2009
Location: Calgary
Posts: 2
Default

Quote:
Originally Posted by Daox View Post
The panel heats up a tank of water. You draw on that water just like you would a conventional water heater.
Hi everybody!

This is my first post, so go easy on me.<EDIT>: it looks like Gary updated the original link June 11 '09, about five days after the last post in this thread.

I'm pretty sure the panel keeps draining back into a (thermal) storage tank, that has a 300' coil of PEX pipe submersed in it. The PEX coil is plumbed inline between the supply service and the hot water tank. When the collector is warming the water in it, it travels through in to the storage tank, and the seperate coil (with potable water) takes on heat from the storage tank, on it's way to the HWT.

I'm not sure if that's right, or makes sense, but here are a couple of pics from a link on the site mentioned above;


PEX coil not to scale, lol. P is for pump and V is for Valve. The valves are there should he need to by-pass the solar collector.

The PEX in the tank with it's inlet and outlet connected to house plumbing.

You can see the white drain pipe in the middle of the picture, at the corner of the storage tank. The (cooler)water gets pumped from the tank bottom up into the collector, then drains (warm) into the top of the tank.

http://builditsolar.com/Experimental/PEXColDHW/Overview.htm

Thanks for the in-depth tour Gary. If I get some time in the Spring, I'll take a crack at this!

alg


(Support EcoRenovator.org & get rid of these annoying ads!)      
 
algernon is offline   Reply With Quote
Old 03-03-10, 02:43 PM   #22 (permalink)
Lurking Renovator
 
Join Date: Mar 2010
Posts: 1
Default

I am a newbie to solar, I have been reading a lot and Gary's design really caught my eye. I live in Vermont with my wife and three daughters (teenage years are coming so hot water is going to be in short supply at my house). I heat my house 90% of the time with a Vermont Castings Defiant wood stove located in the basement next to my current hot water tank. I also have an oil fired boiler that I use for heating my DHW and base board heat. I am in the process of installing a secondary hot water tank that will feed the primary tank. The water in the secondary tank (80 gallon electric tank that will not be wired) will be preheated by circulating water through a heat exchanger on the back of my woodstove.

I had seen quite a few people that had put an exchanger inside the stove, but that just scared me, we lose power occasionally and I really did not want to come home one day and find pieces of my stove in the living room because it blew up.

So now you know a little about my setup, here is the solar question. Since I have a way to heat my hot water in the winter months with the woodstove heat exchanger could I use Gary’s PEX panel design to preheat my water in the summer months? I know it would have to be drained in the winter and I would probably move it into the garage. It would be considered a Direct Pumped System.

I know a couple of things would need changing, like the fact that I can’t use PEX-AL-PEX for potable water so I would probably use 1/2” PEX with elbow on each end. I would also have to put a pressure release valve and probably an air vent at the top of the panel where the water exits. I would utilize the same secondary tank and circulator so I think I am looking at about $300 to create the panel with enough pipe to bring it into the cellar. Any thoughts?


I had a couple of links to show examples but it would not allow me to post them, so if you have a question on my design please email me or post a reply. Thanks
Trevor is offline   Reply With Quote
Old 03-07-10, 09:10 PM   #23 (permalink)
Joe
Lurking Renovator
 
Join Date: Jan 2010
Posts: 18
Default

Quote:
Originally Posted by Trevor View Post
I know a couple of things would need changing, like the fact that I cant use PEX-AL-PEX for potable water so I would probably use 1/2 PEX with elbow on each end. I would also have to put a pressure release valve and probably an air vent at the top of the panel where the water exits. I would utilize the same secondary tank and circulator so I think I am looking at about $300 to create the panel with enough pipe to bring it into the cellar. Any thoughts?


I had a couple of links to show examples but it would not allow me to post them, so if you have a question on my design please email me or post a reply. Thanks
Hi Trevor, if you will be circulating potable water through it I would recommend you use the copper style collector as normal pex wont hold up. you will need a temp differential controller(turns pump on when collector is hotter then the tank and off when tank max temp is reached) and a pump designed to circulate pressurised water (gerfundos?) when max tank temp is reached the pump stops running and the water just bakes in the collector(stagnate condition) and can get up to about 200* or more in strong sun, and I don't know about you but I have 80 psi water pressure and that would put me right at the 200* 80psi limit of standard pex. I think what would work good for you is batch heater as long as you drain it before the freezing weather or just build the $1k drain back system and not use the extra hot water heater. This is right off Gary's site:
*

It is easily bent in to tight turns AND it retains its shape without spring back. This is a very nice feature.

*

It has higher working and burst pressures than ordinary PEX.
The PEX-AL-PEX I used (Mr. PEX) is rated for 160 psi at 200F.
Standard PEX is rated at 80 psi at 200F, and 160 psi at 73F.

*

It has better thermal conductivity that regular PEX -- this should result in somewhat better heat transfer from the aluminum fins through the PEX to the water.
PEX-AL-PEX 3.1 BTU/h-ft F for half inch tubing
PEX 2.6 BTU/h-ft-F for half inch tubing

*

It has a much lower coefficient of thermal expansion than PEX, and is more compatible with the expansion rate of the metal fins.

*

It may be somewhat more tolerant of freezing. It will probably withstand several freeze thaw cycles, BUT will NOT withstand continual freeze thaw cycles.

so regular pex would be less efficient and wouldn't be a good idea to subject it to such conditions. By the way I have seen the pictures of the blown up wood stoves and they all didn't put a pressure relief valve in-between the shut off valves and the heat exchanger
Joe is offline   Reply With Quote
Reply

Tags
hot water, solar

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Smoke Alarms
Visit SDFireAlarms.co.uk for Ionisation or Optical Smoke Alarms.
House prices in scotland
This site will help you understand house prices in Scotland and let you view similar properties and their past transactions.
Windows
Check out everest.co.uk to make your home warmer, quieter, and more secure with “the best” Casement, Cottage, Dual turn, windows.
Mattress
In need of a new mattress? Visit Beds Warehouse for matresses of all ranges. Click here now!

All times are GMT -5. The time now is 11:34 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.3.2
Ad Management by RedTyger
Inactive Reminders By Icora Web Design