Quote:
Originally Posted by buffalobillpatrick View Post
DEnd

What you are saying is true, "IF" the boiler turned on whenever a thermostat called for heat. Sadly this is how many systems are implemented.
It's true regardless. A 50% duty cycle at design conditions is Short Cycling. While the 79 gallon buffer tank may keep burn times long enough to avoid most condensation issues, but you are still wasting energy. Every time you start the boiler you are wasting energy, because the initial energy is needed to bring the system up to operating temps before it can put out heat, and also due to incomplete combustion as it warms up. Energy is also wasted at the end of combustion due to incomplete combustion. This is where Mod-Con boilers are able to save energy, they are able to better supply heat at the rate of heat loss.

In a low heat loss home, a lot of times Domestic hot water demand can outstrip heat demand, the buffer tank can help a lower output boiler keep up with demand. If there is a huge mismatch it may be better to separate out the uses. This allows the system to be more flexible, and possibly increasing system efficiency.

Also Solar Thermal? Unless you are hard up on solar access it's just not worth it. It may be cheap enough if you build you own flat plate collectors, but factor in your time, and the decreased system reliability and I doubt the cost/benefit is there.

DEnd is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiTweet this Post!
Reply With Quote
Old 01-11-18, 12:16 PM   #12
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 593
Thanks: 812
Thanked 58 Times in 54 Posts
Default

Dend, your:
“It's true regardless. A 50% duty cycle at design conditions is Short Cycling.”

U R confusing a boiler that is oversized for the home heating load at “design” temperature
(2*F) here, with Short Cycling.

It’s not oversized for my house DHW load when 2 showers are on or filling a large bathtub.


Hot Rod Rohr (HR) who is Caleffi’s USA technical communications lead defines “Short Cycle” as:

“More than 3 boiler cycles per hour or boiler cycles less than 10 minutes in length.”

“If you look at it from simply a cycle life of the components, regardless of efficiency, that 10 minute on/ off is the guideline I have used.”


My boiler firing time will be: 30 minutes minimum in Summer, and much longer in Winter.

BTW, my boiler don’t waste heat at the end of a cycle, it burns clean until the moment that the gas valve is closed and then the residual boiler heat from the cast iron is pulled out & used by an adjustable post purge cycle of the boiler pump.

ModCons never again!


Last edited by buffalobillpatrick; Yesterday at 09:57 AM..
buffalobillpatrick is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiTweet this Post!
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -5. The time now is 02:56 AM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2018, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Ad Management by RedTyger
Inactive Reminders By Icora Web Design