Old 08-20-15, 04:03 PM   #1
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default best adaptor for generator connections

Am redoing some connections to my electrical infrastructure and would like some input.

I have ~ 600 A one phase service distributed first to a manual transfer switch and then that goes to three subpanels. Farm house, guest house and barns/shop (200 A each).

Have a 7.5 kW battery electric start gasoline generator and a 15 kW PTO (power take off) generator. Currently, I use a "double male" (dangerous) to hook things up with the 7.5 kW through a 50A female electric stove type receptacle in the shop. This is the one I use with my welders. I have not had to use the PTO generator yet.

I really dislike exposed "male to male" electrical connectors as there is a very hot and dangerous end when you have it connected to the running generator. Have done this "safely", but I would rather replace it with a proper connector. If I am not home, I do not want my wife or someone else to be hooking up a live hot male connector in the dark.

I know to first turn the transfer switch to remove grid, turn off all sub-panels, hook up dead wire ends to receptacle connector and generator, turn generator on and then turn on panels and specific circuits on each panel that are absolutely necessary.

Have been looking at 50 A Reliance (PBN50) female receptacle at a cost of ~ $75. But before I do I thought I would ask the group for their thoughts. This would mount to the side of the manual 600 A transfer switch.

Reliance Controls PBN50 50-Amp Power Inlet Box Non-Metallic

The 7.5 kW generator works great to start and run the deep well water pump, freezers, a few lights and fridge. The problem with it is that it just sucks gas down (only a three hour run time on the 4 gallon tank) and filling it with gas in the middle of the night, in the dark can result in unpleasantness . . . .

An el Nino looms and in in those Oklahoma winters we get BIG ice storms and can be out of power for days due to downed power grid lines. A few years ago we had power after a big ice storm, but just to the west people were out for five weeks . . . .

The nice thing about the 15 kW PTO generator is that I have plenty of diesel fuel storage (several 50 gallon drums) and the 80 HP diesel tractor has a large fuel tank. I can then run my geothermal heat pumps and almost anything else with 15 kW for about 6-7 hours without refilling with fuel.

In the future I may put in a Generac unit that automatically turns on, but for now I can use my existing generators.

Thoughts on plugs/receptacles, etc? TIA


Steve

__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 08-21-15, 03:58 AM   #2
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Your interest in replacing the suicide cord is warranted and highly recommended as a first priority. Those things are lethal and a temporary rig to be used in very limited circumstances. A transfer panel is a much safer and better solution.
jeff5may is offline   Reply With Quote
Old 08-21-15, 09:41 AM   #3
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Just observed something interesting. 30A receptacles have four prongs (hot, hot, neutral and ground) yet 50A receptacles have only three (hot, hot and neutral).

Why is this?

Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 08-21-15, 10:19 AM   #4
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Here are links to Generac boxes and plugs.

http://www.amazon.com/dp/B009TNTZUK/...95ea93df3097_S

http://www.amazon.com/Generac-6331-5...ZSQ0F6XGC3A39E

The box is ~ $67 and the plug is ~ $45.

Again, I will mount this box on the manual transfer switch case and install the plug on a three wire (copper, 6G stranded) flexible cord.

This will eliminate any exposed "hot" ends and will be a lot safer than the "suicide cord" (thanks Jeff, I hadn't heard that term, but it is VERY appropriate).

If anyone has a better/safer/cheaper approach, please let me know. TIA


Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 08-30-15, 10:55 PM   #5
gtojohn
Journeyman EcoRenovator
 
gtojohn's Avatar
 
Join Date: Jul 2014
Location: Austin, TX
Posts: 314
Thanks: 39
Thanked 50 Times in 45 Posts
Default

For around $100 I don't think you'll find anything safer than the Reliance. They do make 4 prong 50amp range cords, still not safe. You might consider a smaller genny for better fuel economy my 5500 can run 7-9 hrs with its 5 gallon tank. Or save a little fuel by lowering your rpm from 3600 to 3000 your frequency goes down to 50hz , electronics should still be happy.

__________________
1.47 kw solar, R-40+ attic insulation, 4 layers radiant barrier, solar attic fan, solar mini pool pump
gtojohn is offline   Reply With Quote
Reply


Tags
connections, generator

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 11:05 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design