#1001 (permalink) |
|
Lurking Renovator
Join Date: Dec 2009
Location: Pensacola Florida
Posts: 15
Thanks: 2
Thanked 0 Times in 0 Posts
|
I have my well drilled to 40 feet and currently designing the heat exchanger.
Thank you AC_Hacker, Ecorenovator, and all other contributors for the excellent information and documentation. charlesfl (Support EcoRenovator.org & get rid of these annoying ads!) |
|
|
|
|
|
#1002 (permalink) | |
|
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 1,698
Thanks: 62
Thanked 140 Times in 105 Posts
|
Quote:
Congratulations on your thermal well! Near Pensacola, are you? I lived for a short time, not too far from Fort Walton Beach, so I'm quite familiar with that sand. It would be very useful if you could share some of the details through descriptions and photos, if you took them, of how you went about drilling in sandy soil like you have there. I know that there are other folks who read this thread, and are from the sunny, sandy South. Your experience could help others, with similar soil conditions, to also be successful. My guess is that you used drilling mud to keep the sand from caving in on your drill string. But you may have discovered an easier way to do it. Fourty feet deep is pretty darn good. I'm also very interested in how you are going about designing and making your heat exchanger. I think that is probably a difficult part of the project for very many people. How many Tons of cooling are you expecting from your unit? I assume that you are going with an air handler for inside your house, although circulating cooling water through ceiling panels would be another approach, if you could find a way to control the condensation problem. I have read quite a few accounts of the use of ceiling panel cooling in European office buildings. Apparently they use humidity sensors (and I would assume de-humidifiers, too) to modulate temperature/humidity so that the dew-point is not reached... otherwise, it would start raining inside. Anyway, good luck on your project! Best regards, -AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
|
|
|
|
|
#1003 (permalink) | |
|
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 1,698
Thanks: 62
Thanked 140 Times in 105 Posts
|
This is a response to a question that originally appeared on the R-290 thread, but I thought it would be good to post it here...
Quote:
Your conversion from R-22 to R-290 or Enviro-safe is correct, but it's still 5 pounds of hydrocarbon refrigerant, so play it safe. Regarding pressure, I found that when I used R-290, the pressures required to get good performance were actually much less than the pressures called out for R-22. For instance, when the R-22 pressures were:
I was getting good performance from R-290 at:
...sometimes even lower. I started with the same pressure for R-290 as were called out for R-22 and when I ran my compressor, I didn't see any evidence of the miracle of refrigeration taking place... in face I was completely crest fallen and was sure that I was a complete failure until I reduced the pressure way down. The unit had a very slow leak and ran my compressor through several days with the vacuum gauges attached and got to see the range at which the setup would work... it was very interesting. I also did some efficiency tests over that range, and that was even more interesting. Another thing, when I was hacking my unit I changed out both HXs, and the overall system volume was significantly changed, so I couldn't rely on weight of refrigerant... I had to go by pressure and performance. -AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
|
|
|
| The Following 2 Users Say Thank You to AC_Hacker For This Useful Post: | Geo NR Gee (11-21-11), sparkchaser (11-21-11) |
|
|
#1004 (permalink) |
|
Jack of all trades
Join Date: Jun 2010
Location: Washington
Posts: 25
Thanks: 3
Thanked 1 Time in 1 Post
|
Hello all,
I was wondering about that! I had read somewhere the pressure and quantity were less than R-22, but I didn't know just how much!
__________________
I'm not cheap, I'm just economical! To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. |
|
|
|
|
|
#1005 (permalink) |
|
Uber EcoRenovator
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 80
Thanks: 0
Thanked 16 Times in 12 Posts
|
This past weekend the homemade GSHP was installed. As you may remember the shop is about 1800 sq ft. and insulated well. The office area is aprox 600 sqft with infloor heat and the balance shop area is to be heated with a air- handler. The heat pump was built around a 2 Ton air-condition compressor. In the test phase it put out about 18KBtu/H. For now the ground loop only has water in-case we decide to change to a 3.5T compressor unit it will be less of a mess. The numbers are as follows: Incoming ground loop temp 55 deg F Out to ground loop 53 Deg F. By these numbers the flow rate is good. The temp out from the GSHP to the shop air handler and infloor heat is 82 Deg F return is 72 Deg. After running for the whole day (8 Hrs) with an outside temp 34 Deg. the shop only made it to 62 Deg F. The office floor only 66 deg. The air handler is putting out air at 78 Deg F. I'm going to let it run through the night 24 Hrs to see if we have maxed out. The electrical energy in is a whopping 1290 watts. If we can make 76 deg in the shop and or infloor temp. I can live with that otherwise a larger source will be needed. If I could ask AC Hacker; do you run your GSHP continually? and what performance do you see.
Randen |
|
|
|
|
|
#1006 (permalink) | |
|
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 1,698
Thanks: 62
Thanked 140 Times in 105 Posts
|
Quote:
Last winter I did a test run, to see how the heat pump and the loop field were working together. I didn't have any kind of thermostat for most of the run, so I left it on, 24/7. I used an automobile radiator for an air handler, because that was all I had, and I put a box fan behind it, blowing on 'medium' speed. I ran the test in my basement which is pretty small, 24 x 15, and the basement has no insulation at all, I haven't done any rigorous air sealing, and there was an opening in the basement to a crawl space that was 16 x 16, no insulation. I would say that only 180 square feet of the 616 square feet of the ceiling in the basement (and crawl space) had directly heated space (70F) above it. The rest of the cieling space was only heated by the heat that leaked out of the heated space (37F to 55F). I was using a loop pump that was moving about 2.3 gallons per minute. My compressor is really miniature, it came out of a 25 pint per day de-humidifier, it draws somewhere in the neighborhood of 400 watts. My conservative guess is that it was putting out around 4000 BTU/hr. Having said all that, it took about three days for my basement to go from it's usual low 40s temperature (for that time of year) to around 60F degrees... which I felt was not an unreasonable temperature for a shop. There was a lot of variation in my basement temperature during that time, partly due to ambient air temperature (I think because the space is almost all underground, this was not so important), and partly due to the effects of the loop field temperature during this test. Because I live in the Pacific Northwest, rain that has come off the Pacific ocean has a major effect on local weather. I noticed that rainfalls carried a lot of heat, and when the rain fell on the ground, that heat passed into the ground, and therefore affected my loop filed temperature in a positive way, and had a noticeable effect on the performance of my heat pump and on the basement temperature. I also learned that a warmish rain would not register in the loop field temperature for maybe three days, but then as it worked it's way down through the ground, I would see an up-tick in loop temperatures and also basement temperatures. an up-tick in loop temperatures might be in the neighborhood of 1 or 2 tenths of a degree, but that would mean an up-tick of maybe 4 to 6 degrees in the basement. At one point, the basement hit 73 degrees and felt uncomfortably warm. (* It was about this time that I broke my arm quite badly, so not much has been done since then. *) So, I don't know if this is what you wanted, but this was how it was. Because I was using air out, I wasn't sure how to measure performance quantitatively... I just went for experiential knowledge. Regarding your system, I would suspect that your air handler is on the small size... this kind of gets back to my rant about low temperature heating and hydronic floors and how low temp heating needs optimized floors and large radiating areas, and all that... I forget exactly what you said about your air handler, I seem to recall that you may have said that you converted it from another type of fuel source to what you are presently using. At any rate, I have read quite a few accounts about people who have plumbed a heat pump into an air handler that was originally meant for fossil fuel, and were disappointed by the results. The reason in that situation is that fossil fuel yields much higher temperatures, so an air handler with a smaller area will work, but if you try to use the same air handler with a lower temperature heat source, it will not put out heat at the same rate. I think it should be pretty easy to see if this could be a remedy for you, you could hook up a few car radiators with fans, in-line with your regular air handler to see if it made any improvement. Another thing to look at is testing and tweaking your heat pump to get maximum performance. Have you looked into subcooling & superheat? Here's a document on it... Another approach would be to run a series of your COP test like you did before, and try tweaking your TXV and also refrigerant pressure level to get maximum heat output... which might be a different 'tuning' than what you'd get with a maximum COP 'tuning'... And, lastly, you may be right, you just might need a bigger compressor. I hope this has been of some help... -AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
|
|
|
|
|
#1007 (permalink) |
|
Uber EcoRenovator
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 80
Thanks: 0
Thanked 16 Times in 12 Posts
|
I had left the GSHP purr away all night. The office floor temp made it to a solid 75 Deg F. The shop area never made it past 62 Deg F The overnight outside temp dipped below freezing with some wind. The ground loop temp didn't change. Although the shop is comfortable enough now but when winter takes a big dip I don't think it will remain so. As AC hacker had suggested I played with the amout of refrigerant charge.With the gauge set installed and the amp meter as well as a digital temp probe on the highside tube a temp of 176 Deg F was read. Adding a little propane slowly got me to 179 Deg F the current draw didn't change much the high side pressure rose 10 psi. As more propane was added the current rose to 7.5 A and the temp dropped. As I removed propane the temp peaked and then dropped again and the current dropped. The sweet spot is 210 psi High 45 psi low 6.4 A and 179 Deg F out to the HX. Well it looks like the verdict is in, we need to step up to the 3.5T compressor. Thanks for the help and inspiration
Randen |
|
|
|
|
|
#1008 (permalink) | |
|
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 1,698
Thanks: 62
Thanked 140 Times in 105 Posts
|
Quote:
You could use it for the 'shoulder season' and use the 3.5T for serious heat. I really like your 'current draw/temp out' approach to optimizing your refrigerant charge, very clear and to-the-point. Best, -AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
|
|
|
|
|
#1009 (permalink) |
|
Helper EcoRenovator
Join Date: Oct 2010
Posts: 91
Thanks: 0
Thanked 4 Times in 3 Posts
|
look here,
you guys had said something about making your own socket fusion ends these are replacement faces. Socket Fusion Faces : TLSF : Tools and Accessories : Geo-Hydro Supply, Ltd. |
|
|
|
| The Following 2 Users Say Thank You to rhino 660 For This Useful Post: | AC_Hacker (11-25-11), Geo NR Gee (11-24-11) |
|
|
#1010 (permalink) |
|
Apprentice EcoRenovator
Join Date: Jan 2011
Location: Seattle
Posts: 151
Thanks: 26
Thanked 2 Times in 2 Posts
|
Rhino 660, way to go. Perfect. Now, I could have turned them on the lathe, had them coated, drilled and well, sometimes its faster to buy them.
(Support EcoRenovator.org & get rid of these annoying ads!) |
|
|
|
![]() |
| Tags |
| air conditioner, diy, gshp, heat pump, homemade |
| Thread Tools | |
| Display Modes | |
|
|