Old 06-09-17, 10:14 PM   #21
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

You can measure the high side pressure to find out. The condensing temperature will follow the high side pressure and vice versa. The corresponding values can be looked up on a PT chart for the refrigerant being used. Any superheated gas leaving the compressor will not fall below its condensation temperature until it has all changed phase. Out of 1000 btu's of heat transfer, 950 or more of those btu's flow as the gas condenses.

On the water side of the heat exchange, it matters which way the water flows versus the refrigerant in the HX. Counterflow yields more heat transfer. Usually, the water will exit a few degrees cooler than the entering refrigerant.

In ChetT's proposed mod to his existing system, a BPHE could be rigged between the outlet of the slab and the inlet of the boiler. When the system first fires up, the water entering the BPHE would be slab dwell temp, and the heat pump would run at max energy savings to preheat the water entering the boiler. As the HP ramps up, the boiler could bridge the gap in capacity. Once the HP provides enough capacity, the boiler could stop for the rest of the cycle. Short cycling the boiler would not cause any adverse side effects.


Last edited by jeff5may; 06-10-17 at 08:20 AM..
jeff5may is offline   Reply With Quote
Old 06-10-17, 01:27 AM   #22
WyrTwister
Master EcoRenovator
 
Join Date: Jun 2013
Location: USA
Posts: 543
Thanks: 6
Thanked 44 Times in 38 Posts
Default

Sorry , do not know .

My MS's do not have an outside service port ( do not know about inside the cabinet ) for the small line ( high pressure when cooling ) . Otherwise you could measure the pressure and interpolate a rough temp range .

God bless
Wyr
WyrTwister is offline   Reply With Quote
Old 06-10-17, 07:30 AM   #23
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by creeky View Post
I sort of skimmed this post. I'll come back to it. But I thought I would add this company. I am not associated ... but they have some add ons that are pretty close to what is described here.

Here's hot water recovery for your domestic hot water off of your heat pump

Will be interested in what you think.
This gizmo is also known as a desuperheater. They work better in cooling season than heating season.
jeff5may is offline   Reply With Quote
Old 06-10-17, 07:45 AM   #24
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by WyrTwister View Post
Sorry , do not know .

My MS's do not have an outside service port ( do not know about inside the cabinet ) for the small line ( high pressure when cooling ) . Otherwise you could measure the pressure and interpolate a rough temp range .

God bless
Wyr
Been there before. See post #8 in this thread. Most all mini-split units only have one service port per zone. Each port floats at whatever pressure the indoor unit is operating. Since the metering device (or devices if multiple circuits exist to connect to multiple indoor units) is inside the outdoor unit, both lines leading indoors are at the same pressure, minus any small pressure drop the indoor HX induces.



As you can see in the illustration, the indoor HX is plain jane as can be. The only elaborate component is not shown: the control system. The two sensors and fan speed control do all the magic indoors. As discussed before, rigging the fan control to run a water circulator and placing the thermometers to jinx the outdoor unit is highly possible. In heating mode, defrost sensing of the indoor coil is a moot point. The vane motor is usually a slave device, and the "pipe" sensor tells the outdoor unit if there is an airflow problem: if insufficient airflow exists, the discharge temperature will not taper off, due to lack of heat dumped. At a certain limit, the control trips on over-temperature.

Last edited by jeff5may; 06-10-17 at 08:30 AM..
jeff5may is offline   Reply With Quote
Old 06-10-17, 04:44 PM   #25
ChetT
Lurking Renovator
 
Join Date: Sep 2014
Location: CA
Posts: 15
Thanks: 0
Thanked 2 Times in 2 Posts
Default

Jeff,
Maybe you don't need to move any temperature sensors. You can use the existing radiant slab thermostat. When the system calls for heat you could fool the inside head unit of the mini/s by faking the ambient temperature sensor input with a low temp resistance. Then the head unit would instruct the compressor to turn on.

ChetT is offline   Reply With Quote
The Following User Says Thank You to ChetT For This Useful Post:
jeff5may (06-10-17)
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:04 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design