So I'm on ACwholesalers trying to pick out a minisplit. The problem is I'm not sure what I need as far as capacity. I'm looking at one large area that is 900 sqft and another small room that is 100 sqft.

This is the 1st floor of a 2 story house. Large porch on the south side so the front door and two front windows will never see direct sun light. No west windows and only a small 3x3' north window. On the east is a glass door and a 3x5' window. 2x6 tight construction with rigid foam board on the outside of the house R11.25. I might be adding spray foam or fiberglass between the studs but I'm not sure right now. Remember there is a 2nd floor that will also be conditioned so no attic heat being added to the 1st floor.

How much AC do I need. 1 ton?

thanks
Austin

dablack is offline   Reply With Quote
Old 01-12-15, 04:00 PM   #2
ecomodded
Supreme EcoRenovator
 
Join Date: Sep 2012
Location: Vancouver Island,Canada.
Posts: 1,037
Thanks: 116
Thanked 100 Times in 87 Posts
Default

Your asking a lot from a one ton , might be better to go with a 1.5 ton / 18000Btu's and use three indoor units.

Just my opinion , I would use a 1 ton for 1 floor only.

How many Heating Btu's are you using now in the winter ? that number will help you size your mini split
ecomodded is offline   Reply With Quote
Old 01-12-15, 05:15 PM   #3
dablack
Helper EcoRenovator
 
Join Date: Jan 2010
Posts: 65
Thanks: 0
Thanked 13 Times in 6 Posts
Default

Yes, the 1 ton would be for one floor only. The 1st floor is about 1000sqft. That is where I'm wanting to use the MS. So does every think 1 ton will cool 1000sqft of well insulated, shaded 1st floor?

It is a new build so I don't have an existing heat requirement. I'm not really worried about heat. It doesn't really get cold here.

Thanks
Austin
dablack is offline   Reply With Quote
Old 01-12-15, 05:21 PM   #4
dablack
Helper EcoRenovator
 
Join Date: Jan 2010
Posts: 65
Thanks: 0
Thanked 13 Times in 6 Posts
Default

This is for east tx. Zip 75785. 97f and crazy humid in the summer.
dablack is offline   Reply With Quote
Old 01-13-15, 02:13 PM   #5
dablack
Helper EcoRenovator
 
Join Date: Jan 2010
Posts: 65
Thanks: 0
Thanked 13 Times in 6 Posts
Default

OK guys. I did a little more research and it looks like in my climate, 1.5 tons is required for 1000sqft. Using various calculators online gave me 17k to 19k BTUs of cooling.
dablack is offline   Reply With Quote
Old 01-14-15, 01:45 AM   #6
gtojohn
Journeyman EcoRenovator
 
gtojohn's Avatar
 
Join Date: Jul 2014
Location: Austin, TX
Posts: 314
Thanks: 39
Thanked 50 Times in 45 Posts
Default

With tight construction and no attic heat load you should be able to get away 1.5 ton. A 2 ton might cost just a little more, use just a little more power but give you a buffer for 100f heat waves. The cost and efficiency on the multi zone units isn't as good as the single zones systems. Personally I would rather buy 2 single zone systems than one multi zone if anything for the redundancy of 2 separate systems.
gtojohn is offline   Reply With Quote
Old 01-14-15, 04:13 AM   #7
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by dablack View Post
OK guys. I did a little more research and it looks like in my climate, 1.5 tons is required for 1000sqft. Using various calculators online gave me 17k to 19k BTUs of cooling.
It really depends on your comfort and zone control needs. A high efficiency 1 to 1 1/2 ton single-zone unit would be the most efficient, as it would literally run constantly during those days of extreme temperature. However, if your living space is very compartmentalized, the comfort will not just leak into the closed off areas. A couple or three of 3/4 to 1 ton units would be nearly as efficient, and offer better zone control (maybe better if unused zones were shut off or set back) and would dehumidify better. They would most likely cost more than a single unit.

A mini-multi zone unit sized to meet your design heat load or better would be a compromise all the way around. Installation would be complex, both with lineset plumbing and electrical control wiring. Zone control would vary with the load and balance of zones demanding heat. Efficiency would also vary with the overall load. Cost would most likely fall in between the other two options.

The main thing to remember is to purchase a name brand unit! Do not be lured into buying some off brand system to save a few dollars. When and if something goes wrong in the future, you want to be able to get service and parts to complete a repair. The knock off manufacturers all have terrible reputations in this department.
jeff5may is offline   Reply With Quote
Old 01-14-15, 03:29 PM   #8
dablack
Helper EcoRenovator
 
Join Date: Jan 2010
Posts: 65
Thanks: 0
Thanked 13 Times in 6 Posts
Default

GTOJohn,
Are you thinking maybe two 3/4 ton systems?

Jeff5may,
I'm not sure where to put the two units if I did go that way.

Layout is attached.

I was thinking of putting the 1.5 ton over the kitchen windown. This is the north side of the house.



Attached Thumbnails
Click image for larger version

Name:	kitchen 1.jpg
Views:	714
Size:	20.3 KB
ID:	4937   Click image for larger version

Name:	kitchen 2.jpg
Views:	694
Size:	20.9 KB
ID:	4938  

Last edited by Daox; 01-14-15 at 03:33 PM.. Reason: more info
dablack is offline   Reply With Quote
Old 01-14-15, 03:41 PM   #9
dablack
Helper EcoRenovator
 
Join Date: Jan 2010
Posts: 65
Thanks: 0
Thanked 13 Times in 6 Posts
Default

Looks like I can get two Gree 22 SEER 9000 BTU units for 834 each (total of $1668)

or one Gree 21 SEER 18000 BTU unit for $1516.


If I went with two units, I would put one over the hutch and one to the right of the sink.

Thoughts?
dablack is offline   Reply With Quote
Old 01-14-15, 09:27 PM   #10
ecomodded
Supreme EcoRenovator
 
Join Date: Sep 2012
Location: Vancouver Island,Canada.
Posts: 1,037
Thanks: 116
Thanked 100 Times in 87 Posts
Default

I like the idea of having 2 units.

Then you can run 1 unit in the less demanding times and 2 units when the weather calls for it.

I would put both my indoor units on a outside wall rather then above the hutch.
My reason being that it would be easier to mount it with the line ,and run the drain.

ecomodded is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 09:02 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design