Old 06-30-10, 09:10 PM   #61
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default Duct Sizing (making it quiet)...

I'm working out the details of the design now.

From reading product literature, it looks like condensation will be an issue. There seem to be various schemes involving sensors and circuitry and "drying cycles", but for now I'm going to plunge ahead and ignore condensation to see just how big a problem it really is.

Since my realization that I have greatly over-sized my core, I have decided to go with a dual-core design. I'll divide the core stack in two, the cores being in series, with the air passing from one core to the next. This will double the distance over which heat exchange will take place, and should approximate a counter-flow heat exchanger.



So the next design issue will be duct sizing... I recall that Piwoslaw posted this:

Quote:
Originally Posted by Piwoslaw View Post
As for air flow, I believe the minimum is 0.5 house volumes per hour, the maximum is either 2 or 4 house volumes per hour (don't remember). When replacing more than 2 (or 4) house volumes per hour the heating/cooling/recovery system may not be able to keep up, leading to noticeable drafts and energy loss. Also, the ducts should be sized to keep air speed below 5 m/s to keep noise down.
There is a wonderful little program called CurveExpert, that is true shareware and does a great job of curve fitting and formula generation.

I tried inputting value tables from HVAC sites, in order to generate an automated formula for you, my reader. Unfortunately my first attempt failed so I found some online calculating pages that will calculate duct sizes from CFM.

Here one for metric

Here's one for US measurements

And here is a table just to double check your results.


The issue here is that if the air in the duct flows too quickly, it goes into turbulent mode and can make a lot of noise. A friend of mine re-did the ductwork in his house and neglected this issue. Silence really is golden.

The ventilation rate I previously calculated was about 15CFM, at least that's what I rounded it up to.

Using the online calculator for US measurements, and using the value of 15 CFM, and using PVC as my duct material, I get a diameter of 2.85 inch ID.


So anything bigger than 2.85 inch will be nice and quiet. Three inch looks to be a winner so long as I keep my runs short. Four inches will just cost me more money and it will require more insulation to be efficient.

Bigger isn't always better.


Regards,

-AC_Hacker

PS: Next is fans

* * *

Attached Thumbnails
Click image for larger version

Name:	duct-size.gif
Views:	8335
Size:	11.3 KB
ID:	821   Click image for larger version

Name:	dual-core.gif
Views:	19423
Size:	9.0 KB
ID:	822   Click image for larger version

Name:	d.gif
Views:	9785
Size:	8.3 KB
ID:	823  

Last edited by AC_Hacker; 06-30-10 at 11:37 PM..
AC_Hacker is offline   Reply With Quote
Old 06-30-10, 09:44 PM   #62
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default ignore condensation??

I've been thinking about how to install a unit, so the core is sitting with
the (filtered) outdoor-air-input (carrying the moist air) at the best angle.

I would want the (moist) air coming into the top of the core, so it will
have gravity (and air pressure) helping push the water droplets down and out of the core.
(Into a drain pan with a hose on the bottom).

The longer water is allowed to sit in those passages, the more likely
that water is going to collect airborne dust particles, pollen & etc.

Once a water droplet filled with particles evaporates, the residue
left from the contaminates can build up and be difficult to remove..

The dew point temperature have been so high these last few weeks,
anything that is cold is instantly wet when left out..

~~
Instead of making more holes in my house, I've been thinking of building
my unit like a window AC. (Custom sized for my windows).
So, it could be installed easily and easily pulled out to be tweaked or cleaned.
The drain hose would just water the flowers below the window..

I like the idea, but how am I going to get that good drain angle with a window rig?? Humm...
Xringer is offline   Reply With Quote
Old 07-01-10, 01:00 AM   #63
Piwoslaw
Super Moderator
 
Piwoslaw's Avatar
 
Join Date: May 2009
Location: Warsaw, Poland
Posts: 960
Thanks: 188
Thanked 110 Times in 86 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
PS: Next is fans
I've read that centrifugal or crossflow fans are most efficient for household ventilation. Also, they should be DC powered:
  • AC powered fans "hum" at the grid's frequency and may cause the whole installation to vibrate,
  • AC fans can cause electromechanical interference,
  • DC can be easily tied into an RE or back-up power installation.
Piwoslaw is offline   Reply With Quote
Old 07-01-10, 12:49 PM   #64
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default When HRV is not an afterthought (a real game changer)


I came across information about a Passivhaus (AKA: Passive House) that was built in Illinois.
The house uses an HRV that is almost the size of a furnace, but uses only a tiny fraction of the energy (NOTE: there is an integrated 1 kWatt resistance heater for severe occasions).


This is the first time I have seen the kind of serious HRV that a Passivhaus would utilize. This really alters the definition of HRV... Now all the others seem like toys.

In this particular project, the Westaflex WAC 250 HRV utilizes a 100 foot ling, 8 inch diameter buried earth tube. The WAC 250 unit has sensors and dampers and can switch the incoming air between earth tube air or straight outside air as the situation demands (wow!).

This PDF has the picture shown below


It looks like there is a real-deal counterflow heat exchanger at the heart of it all (or could it be a dual-crossflow?).

I think I finally understand why someone would build a house around a HRV, especially if it was one of these.


Regards,

-AC_Hacker

* * *
Attached Thumbnails
Click image for larger version

Name:	Westaflex WAC 250.jpg
Views:	12129
Size:	49.9 KB
ID:	824   Click image for larger version

Name:	Westaflex WAC 250(b).jpg
Views:	9640
Size:	7.9 KB
ID:	825  
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
jeff5may (02-09-21)
Old 07-01-10, 01:05 PM   #65
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Wow, that is sweet lol. Thanks for posting that info. I've seen that house before and love it. I didn't know of the monster HRV in it though.
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 07-01-10, 01:06 PM   #66
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default Fans...

Quote:
Originally Posted by Piwoslaw View Post
I've read that centrifugal or crossflow fans are most efficient for household ventilation. Also, they should be DC powered:
  • AC powered fans "hum" at the grid's frequency and may cause the whole installation to vibrate,
  • AC fans can cause electromechanical interference,
  • DC can be easily tied into an RE or back-up power installation.
Yes, quite right.

At this point, since my application is so undemanding, I'm considering a pair of 3 inch fans.


But I'm also looking into cross flow fans (AKA: tangential flow).


I also investigated Pulse Width Modulated fans...


...but the energy used by the above fans is so small that energy savings would be very small.


Regards,

-AC_Hacker
Attached Thumbnails
Click image for larger version

Name:	fan-axial.jpg
Views:	9210
Size:	92.5 KB
ID:	826   Click image for larger version

Name:	fan-cross-flow.jpg
Views:	10175
Size:	19.4 KB
ID:	827   Click image for larger version

Name:	kamapwm.jpg
Views:	9128
Size:	29.6 KB
ID:	828  

Last edited by AC_Hacker; 07-01-10 at 02:37 PM..
AC_Hacker is offline   Reply With Quote
Old 07-01-10, 01:48 PM   #67
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default Windows.air.exchange

Since I'm thinking small (and no new holes in the walls), I looked around and found this.
Amazon.com: Bionaire BAP336-U EverFresh Air Exchange System: Kitchen & Dining

I'm not sure how this works, and the from factor is 'out there',
but it shows that my idea of a DIY window mounted unit, wasn't very original.

But that's not going to stop me from trying to figure out how to make one..
Xringer is offline   Reply With Quote
Old 07-01-10, 02:05 PM   #68
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default "Fresh Air" Mini-Split

Quote:
Originally Posted by Xringer View Post
Since I'm thinking small (and no new holes in the walls), I looked around and found this.
Amazon.com: Bionaire BAP336-U EverFresh Air Exchange System: Kitchen & Dining

I'm not sure how this works, and the from factor is 'out there',
but it shows that my idea of a DIY window mounted unit, wasn't very original.

But that's not going to stop me from trying to figure out how to make one..
I noticed that the latest Mini Splits are featuring "Fresh Air".

Search for the "Fresh Air" term, download the appropriate PDF, you might be able to do a "Fresh Air" hack on yours.

-AC_Hacker
AC_Hacker is offline   Reply With Quote
Old 07-01-10, 02:47 PM   #69
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

No way my wife is going to let me touch that Sanyo! She loves that thing!

Plus, there is no venting as you well know.. Only an Ion generator (whatever that does).

Your dual core diagram above has given me a clue about core mounting
(in a window unit) that will allow the core to drain..
Xringer is offline   Reply With Quote
Old 07-01-10, 06:49 PM   #70
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default German Counterflow Heat Exchanger...

A design that is different from the cross-flow types.


Klingenburg GmbH - Energy Recovery - Counterflow plate heat exchanger

Appears to be very similar to the core used in the Westaflex mentioned earlier.

Don't overlook this link, it has lots of interesting literature.

Here's a grab from one of the the documents above.


The company appears to be in the business of selling high efficiency counterflow cores.

Regards,

-Jim

Attached Thumbnails
Click image for larger version

Name:	cross-flow-core-specs.gif
Views:	10786
Size:	16.3 KB
ID:	832   Click image for larger version

Name:	Dimension-GS_1.jpg
Views:	10928
Size:	52.7 KB
ID:	833  

Last edited by AC_Hacker; 07-01-10 at 08:09 PM..
AC_Hacker is offline   Reply With Quote
Reply


Tags
erv, heat recovery, hrv

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:02 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design