HI cholcombe
The short cycling is usually caused by the heat anticiapitor inside the thermostat. It adds a small bit of heat to keep the thermostat from overshooting ,but it cools quickly ~< 1 to 2 minutes,causing a call for heat(short cycling). They are adjustable, a millamp setting ~.1 to 1.5 milliamps is usually found. A reading is taken of the thermostat circuit and that is used as a baseline/first setting. They also usually have the words longer/shorter marked , moving it one or two marks at a time should stop the short cycling.(toward longer) Old thermostats also can do this do to a accumulation of dust on the bulb or because the bimetal strip has gone through so many on off cycles it becomes "sprung".
Also I'm assuming this is a mercury bulb thermometer,it also has to be level if you had it off the wall for remodeling.
It's possible it's a aquastat by my money would be on the T-stat.
Digital based thermostats use algorithms to anticapate heat , and the better models can actually "Learn" not to short cycle or over shoot.